Jon Bendtsen
2017-Apr-03 14:24 UTC
[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
Hi
debian jessie, nut 2.7.2-4
APC Smart-UPS 1500 connected through USB, running nut driver usbhid-ups
This UPS powers my switches, internet connection and my monitor server that
monitors this and my other UPSes + runs smokeping and nagios.
But recently a powerloss seemed to have shutdown my monitor PC immediately, so
it did not shut down the other servers cleanly. Power seem to be lost
immediately.
But my APC Smart-UPS 1500 always reported everything OK.
output from CGI scripts
APC Smart-UPS 1500 - powers switches and routers in little rack +++ also this
server dkfitlet Smart-UPS 1500 ONLINE
100 % 227.5 227.5 20.8 % 39.6 ?C 00:17:00 All data
UPS Model: Smart-UPS 1500
Status: ONLINE
Runtime: 00:17:00
Battery: 27.1 V
Input: 226.0 V
Output: 226.0 V
0.94 A
50.0 Hz
when I go into treemode though, I see something interesting
APC Smart-UPS 1500 - powers switches and routers in little rack +++ also this
server dkfitlet
battery.charge : 100
battery.charge.low : 10
battery.charge.warning : 50
battery.mfr.date : 2005/08/26
battery.runtime : 1020
battery.runtime.low : 120
battery.temperature : 39.6
battery.type : PbAc
battery.voltage : 27.1
battery.voltage.nominal : 24.0
device.mfr : American Power Conversion
device.model : Smart-UPS 1500
device.serial : AS0535132782
device.type : ups
driver.name : usbhid-ups
driver.parameter.pollfreq : 30
driver.parameter.pollinterval : 2
driver.parameter.port : auto
driver.parameter.serial : AS0535132782
driver.version : 2.7.2
driver.version.data : APC HID 0.95
driver.version.internal : 0.38
input.sensitivity : high
input.transfer.high : 253
input.transfer.low : 208
input.voltage : 226.0
output.current : 0.94
output.frequency : 50.0
output.voltage : 226.0
output.voltage.nominal : 230.0
ups.alarm : No battery installed!
ups.beeper.status : enabled
ups.delay.shutdown : 20
ups.delay.start : 30
ups.firmware : 653.12.I
ups.firmware.aux : 4.2
ups.load : 20.8
ups.mfr : American Power Conversion
ups.mfr.date : 2005/08/26
ups.model : Smart-UPS 1500
ups.productid : 0002
ups.serial : AS0535132782
ups.status : ALARM OL
ups.test.result : No test initiated
ups.timer.reboot : -1
ups.timer.shutdown : -1
ups.timer.start : -1
ups.vendorid : 051d
what? no battery installed, and the status is ALARM? how come NUT doesnt report
this?
root at dkfitlet:/etc/nut# upslog -s apc1500 -l -
Network UPS Tools upslog 2.7.2
logging status of apc1500 to - (30s intervals)
Init SSL without certificate database
20170403 154055 100 230.4 21.4 [ALARM OL] NA NA
20170403 154125 100 230.4 20.8 [ALARM OL] NA NA
20170403 154155 100 230.4 21.4 [ALARM OL] NA NA
root at dkfitlet:/etc/nut# upsmon -DDD
Network UPS Tools upsmon 2.7.2
kill: No such process
0.000000 UPS: apc1500 at localhost (monitoring only)
0.000214 UPS: Smart-UPS_3000 at localhost (monitoring only)
0.000328 UPS: R3000XR at localhost (monitoring only)
0.001278 Using power down flag file /etc/killpower
0.002126 debug level is '3'
0.005831 Init SSL without certificate database
0.011754 Trying to connect to UPS [apc1500 at localhost]
0.013150 Can not connect to localhost in SSL, continue uncrypted
0.013909 Logged into UPS apc1500 at localhost
0.014384 pollups: apc1500 at localhost
0.014501 get_var: apc1500 at localhost / status
0.014889 parse_status: [ALARM OL]
0.015012 parsing: [ALARM]
0.015100 parsing: [OL]
0.015181 ups_on_line: apc1500 at localhost (first time)
notice the value of parsing, first it is ALARM, and then OL. But if only the
last value is returned, then everything seems okay and NUT never reports the
issue?
for my other UPS'es it looks like this, only ever having OL as value.
0.015265 Trying to connect to UPS [Smart-UPS_3000 at localhost]
0.016294 Can not connect to localhost in SSL, continue uncrypted
0.017190 Logged into UPS Smart-UPS_3000 at localhost
0.017673 pollups: Smart-UPS_3000 at localhost
0.017779 get_var: Smart-UPS_3000 at localhost / status
0.018083 parse_status: [OL]
0.018178 parsing: [OL]
0.018261 ups_on_line: Smart-UPS_3000 at localhost (first time)
0.018344 Trying to connect to UPS [R3000XR at localhost]
0.019224 Can not connect to localhost in SSL, continue uncrypted
0.020028 Logged into UPS R3000XR at localhost
0.020600 pollups: R3000XR at localhost
0.020704 get_var: R3000XR at localhost / status
0.021046 parse_status: [OL]
0.021144 parsing: [OL]
0.021228 ups_on_line: R3000XR at localhost (first time)
JonB
Roger Price
2017-Apr-03 15:10 UTC
[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
On Mon, 3 Apr 2017, Jon Bendtsen wrote:> Power seem to be lost immediately. > But my APC Smart-UPS 1500 always reported everything OK. > battery.charge : 100...> battery.mfr.date : 2005/08/26Hi, Could you confirm that the battery is nearly 12 years old? Roger
Stuart Gathman
2017-Apr-03 15:20 UTC
[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
On 04/03/2017 11:10 AM, Roger Price wrote:> On Mon, 3 Apr 2017, Jon Bendtsen wrote: > >> Power seem to be lost immediately. >> But my APC Smart-UPS 1500 always reported everything OK. >> battery.charge : 100 > ... >> battery.mfr.date : 2005/08/26 > > Hi, Could you confirm that the battery is nearly 12 years old? RogerSure, but the issue is that the nut driver and upsd are correctly reporting an ALARM condition, but upsmon is not reacting to it. I don't see offhand anything in upsmon.conf to do something with ALARM. I suggest: 1) replacing the battery ASAP (or buy a modern AVR UPS for not much more) 2) can we simulate an ALARM condition with the dummy-ups driver to debug upsmon (or its configuration)?
Roger Price
2017-Apr-03 15:24 UTC
[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
On Mon, 3 Apr 2017, Jon Bendtsen wrote:> On 03/04/17 17.10, Roger Price wrote: >> On Mon, 3 Apr 2017, Jon Bendtsen wrote: >> >>> Power seem to be lost immediately. >>> But my APC Smart-UPS 1500 always reported everything OK. >>> battery.charge : 100 >> ... >>> battery.mfr.date : 2005/08/26 >> >> Hi, Could you confirm that the battery is nearly 12 years old? Roger > > yeah, it most likely is that oldThat's probably the cause of the immediate power loss. A new battery should fix the problem. Roger
Jon Bendtsen
2017-Apr-03 15:41 UTC
[Nut-upsuser] battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
On 03/04/17 17.24, Roger Price wrote:> On Mon, 3 Apr 2017, Jon Bendtsen wrote: > >> On 03/04/17 17.10, Roger Price wrote: >>> On Mon, 3 Apr 2017, Jon Bendtsen wrote: >>> >>>> Power seem to be lost immediately. >>>> But my APC Smart-UPS 1500 always reported everything OK. >>>> battery.charge : 100 >>> ... >>>> battery.mfr.date : 2005/08/26 >>> >>> Hi, Could you confirm that the battery is nearly 12 years old? Roger >> >> yeah, it most likely is that old > > That's probably the cause of the immediate power loss. A new battery should fix > the problem. Rogeryeah a new battery will most likely make it go away. However, that is not why I wrote the email. I wrote the email because I want NUT to tell me much more clearly that something is wrong, and NUT currently does not do that. JonB
Reasonably Related Threads
- battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
- battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
- battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
- battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error
- battery not installed, but battery still 100% and NUT 2.7.2-4 does not catch this and report a error