Mārtiņš Puķītis
2013-Jun-08 16:57 UTC
[Nut-upsuser] several problems with Powercom BNT-500AP
Thanks for the support. Here's list of when transition to battery with return to utility power within a few seconds occurred in last few days: Wednesday 1:41 11:48 11:54 12:59 13:42 14:42 18:13 18:14 Thursday 5:23 Friday 5:12 7:39 7:43 Saturday 7:34 Here's list of when messages that battery needs replacement occurred: Wednesday 20:34 Thursday 9:07 23:09 Friday 18:25 Saturday 7:32 19:47 I'll take a longer driver log. This page (http://www.networkupstools.org/support.html) says that to take a driver log NUT should be stopped, so I won't be able to tell when these events occurred within a driver log. -----Original Message----- From: Charles Lepple [mailto:clepple at gmail.com] Sent: Saturday, June 08, 2013 6:07 AM To: M?rti?? Pu??tis Cc: nut-upsuser lists.alioth.debian.org Subject: Re: [Nut-upsuser] several problems with Powercom BNT-500AP On Jun 5, 2013, at 11:49 AM, M?rti?? Pu??tis wrote:> Driver debug output attached.The debug output looks normal (many devices do not implement the interrupt pipe; hence, the timeouts). Unfortunately, we might need the log over a longer period of time, including your observations as to when various events occurred (such as transitions to battery). -- Charles Lepple clepple at gmail
Charles Lepple
2013-Jun-08 19:48 UTC
[Nut-upsuser] several problems with Powercom BNT-500AP
On Jun 8, 2013, at 12:57 PM, M?rti?? Pu??tis wrote:> I'll take a longer driver log. This page (http://www.networkupstools.org/support.html) says that to take a driver log NUT should be stopped, so I won't be able to tell when these events occurred within a driver log.Hmm, I didn't realize it said that, but I think that's to prevent having two copies of the same driver running at the same time. (That's even more difficult to decipher from one log alone.) You can either just restart the driver, or restart upsd after stopping everything. In either case, I was thinking that it would be useful to know where *in the longer log* the events occur. Then we can look to see if the UPS is returning bad information, or if the driver is experiencing an error condition. -- Charles Lepple clepple at gmail
Mārtiņš Puķītis
2013-Jun-10 17:05 UTC
[Nut-upsuser] several problems with Powercom BNT-500AP
I took the log. Here's what happened.
Broadcast Message from nut at rasp
(somewhere) at 16:18 ...
UPS BNT500AP at localhost battery needs to be replaced
occurred when for the first time value "1" was read as
"UPS.PowerSummary.PresentStatus.NeedReplacement", on this line:
6409.240690 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input,
ReportID: 0x0a, Offset: 6, Size: 1, Value: 1
It happened for 9 times, but the message appeared only on first.
Broadcast Message from nut at rasp
(somewhere) at 17:33 ...
UPS BNT500AP at localhost on battery
occurred when UPS.PowerSummary.PresentStatus.ACPresent turned to 0 on this line:
10921.069403 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
Broadcast Message from nut at rasp
(somewhere) at 17:33 ...
UPS BNT500AP at localhost on line power
There were 3 more "on battery" events at 2:31:
43194.030619 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature,
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
Here I also see a suspisious frequency value 70. How is this possible?
43194.046966 Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, Offset:
0, Size: 8, Value: 70
At 2:58:
44790.984549 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
Here all voltages and frequencies are OK, so I don't understand why
ACPresent is 0.
44790.374516 Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, Offset: 0,
Size: 16, Value: 232
44790.375512 Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, Offset:
0, Size: 8, Value: 50
44790.376535 Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, Offset: 0,
Size: 16, Value: 232
44790.377511 Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, Offset:
0, Size: 8, Value: 50
and at 6:15:
56597.541128 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input,
ReportID: 0x0a, Offset: 2, Size: 1, Value: 0
At 6:15 I also got "Low battery" event that triggered Raspberry pi
shutdown, but I don't see a reason for that in the driver log.
When it happened, the UPS started beeping every 2 seconds and I could silence it
by pressing the power button, as written in user manual. I was only able to
silence it by shutting down completely. By the way, the first time it happened
also at about the same time.
I'm not able to post the log, because even compressed it is more than 1 MB.
-----Original Message-----
From: Charles Lepple [mailto:clepple at gmail.com]
Sent: Saturday, June 08, 2013 10:49 PM
To: M?rti?? Pu??tis
Cc: 'nut-upsuser lists.alioth.debian.org'
Subject: Re: [Nut-upsuser] several problems with Powercom BNT-500AP
On Jun 8, 2013, at 12:57 PM, M?rti?? Pu??tis wrote:
> I'll take a longer driver log. This page
(http://www.networkupstools.org/support.html) says that to take a driver log NUT
should be stopped, so I won't be able to tell when these events occurred
within a driver log.
Hmm, I didn't realize it said that, but I think that's to prevent having
two copies of the same driver running at the same time. (That's even more
difficult to decipher from one log alone.)
You can either just restart the driver, or restart upsd after stopping
everything.
In either case, I was thinking that it would be useful to know where *in the
longer log* the events occur. Then we can look to see if the UPS is returning
bad information, or if the driver is experiencing an error condition.
--
Charles Lepple
clepple at gmail