I am running a home box (600watt total load, may expand to 800-900) and I need a UPS that can sustain power to that for at least 20 min, but I want as much time as I can get. Does anyone on the list have a similar setup with a UPS that was easy to set up with NUT? Generally speaking, what mfrs. and models are very well supported? Which should I avoid at all costs? I know this seems like something that would be in the archives, but my searches thus far have been fruitless. Thanks in advance! --Clay
Arjen de Korte
2006-Jun-03 17:06 UTC
[Nut-upsuser] Recommended UPS to buy for use with NUT?
Clay Barnes wrote:> I am running a home box (600watt total load, may expand to 800-900) and > I need a UPS that can sustain power to that for at least 20 min, but > I want as much time as I can get.Is that rated load, or actual load? That seems like an awful lot of power for a single system. And unless you've a very complicated shutdown procedure, 20 minutes looks like a very long runtime. If you need that much runtime, consider if you're not better served by a smaller (in terms of runtime) capacity UPS backed by a petrol (or diesel) generator (which will give you hours/days/weeks of runtime, depending on the amount of fuel in the tank). [...]> Generally speaking, what mfrs. and models are very well supported?The website has a nice section on that http://www.networkupstools.org/compat/ It badly needs updating, but if your UPS is listed there, it is supported by NUT (check the driver documentation for the level of support). If you want optimum support, MGE seems to be a good choice however, since they officially support NUT (through Arnaud Quette).> Which should I avoid at all costs?The ones not listed in above mentioned lists. Regards, Arjen