Todd Benivegna
2020-Aug-12  02:29 UTC
[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
Thanks Manuel. I’m following that guide but am now stuck when checking to make sure the nut-sever and nut-client are up and working. I got this: proton at proton:~$ service nut-server status nut-server.service - Network UPS Tools - power devices information server Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 18s ago Process: 1537 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) Warning: some journal files were not opened due to insufficient permissions. proton at proton:~$ service nut-client status nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; vendor preset: enabled) Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 50s ago Process: 1543 ExecStart=/sbin/upsmon (code=exited, status=1/FAILURE) Warning: some journal files were not opened due to insufficient permissions. Do I have incorrect permission on the conf files? I did change this a while back. Why should the default permissions be on the nut folder and the files in the nut folder? I changed from 555 to 640 I believe. proton at proton:~$ sudo ls -la /etc/nut total 60 drw-r----- 2 root nut 4096 Aug 11 22:13 . drwxr-xr-x 147 root root 12288 Aug 11 22:02 .. -rw-r----- 1 root nut 1543 Aug 11 22:13 nut.conf -rw-r----- 1 root nut 5615 Aug 11 21:59 ups.conf -rw-r----- 1 root nut 4601 Aug 11 22:04 upsd.conf -rw-r----- 1 root nut 2466 Aug 11 22:09 upsd.users -rw-r----- 1 root nut 15479 Aug 11 22:12 upsmon.conf -rw-r----- 1 root nut 3879 Feb 8 2020 upssched.conf -- Todd Benivegna // todd at benivegna.com On Aug 11, 2020, 9:09 PM -0400, Manuel Wolfshant <wolfy at nobugconsulting.ro>, wrote:> On 8/12/20 3:55 AM, Todd Benivegna wrote: > > Manuel, > > > > You are absolutely right. I think this is all the Synology just being > > very dumb. I guess those are my only two options at this point. > > > > I have no idea on how to set up the NUT server though on one of my > > NUCs or my Pi. Do you know any good guides out there? > > there are literally tons of guides. for instance: > > https://www.reddit.com/r/homelab/comments/5ssb5h/ups_server_on_raspberry_pi/ > and scroll down to configuring, past the apt install step (which you > already did ) > > basically all you need is to edit a few files below /etc/nut/ . takes 5 > min top > > > > I’m guessing it’s easy enough to edit upsmon.conf on the Synology in > > order to get that to become a slave; I think would be all that’s > > required for the Synology NAS. > > > > Yeah I saw that. Makes no sense. I can Wireshark it, however even if > > I find the cause, I’d still have to go to Synology for resolution, > > which I doubt will ever get fixed. Even if they do, I doubt it’d be > > any time soon. Maybe that’s me being pessimistic, I don’t know, but I > > just don’t if I have the time or energy for all that! > > > no need to wireshark any more, we already know that it sends bogus FSD > > > > _______________________________________________ > Nut-upsuser mailing list > Nut-upsuser at alioth-lists.debian.net > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser-------------- next part -------------- An HTML attachment was scrubbed... URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200811/f88dfe24/attachment.html>
Todd Benivegna
2020-Aug-12  04:11 UTC
[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
Ok, so just a follow-up to my last email; still following that guide, which is great…. Just stuck on getting the nut-server service starting automatically. Got everything else working. I’ve been able to get the nut-client starting up automatically at boot up (I had a missing “1” in upsmon.conf. Oooops!) However, I cannot get nut-server service to start-up automatically still. proton at proton:~$ service nut-server status nut-server.service - Network UPS Tools - power devices information server Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) Active: failed (Result: exit-code) since Tue 2020-08-11 23:43:55 EDT; 2min 0s ago Process: 1559 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) proton at proton:~$ service nut-client status nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; vendor preset: enabled) Active: active (running) since Tue 2020-08-11 23:43:55 EDT; 2min 7s ago Process: 1567 ExecStart=/sbin/upsmon (code=exited, status=0/SUCCESS) Main PID: 1570 (upsmon) Tasks: 2 (limit: 9019) CGroup: /system.slice/nut-monitor.service 1569 /lib/nut/upsmon 1570 /lib/nut/upsmon Warning: some journal files were not opened due to insufficient permissions. I can get it to start manually by doing "sudo service nut-server restart". Then it starts up…. Just starts up and all is good. proton at proton:~$ sudo service nut-server status nut-server.service - Network UPS Tools - power devices information server Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) Active: active (running) since Tue 2020-08-11 23:49:50 EDT; 12s ago Process: 2949 ExecStart=/sbin/upsd (code=exited, status=0/SUCCESS) Main PID: 2950 (upsd) Tasks: 1 (limit: 9019) CGroup: /system.slice/nut-server.service 2950 /lib/nut/upsd Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups Aug 11 23:49:50 proton upsd[2950]: Startup successful Aug 11 23:49:50 proton systemd[1]: Started Network UPS Tools - power devices information server. Aug 11 23:49:50 proton upsd[2950]: User upsmon_local at 127.0.0.1 logged into UPS [ups] Aug 11 23:49:51 proton upsd[2950]: User monuser at 192.168.1.70 logged into UPS [ups] Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.30 logged into UPS [ups] Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.20 logged into UPS [ups] Here is my upsd.conf: LISTEN 127.0.0.1 3493 LISTEN 192.168.1.31 3493 Could it be a permissions issue? Weird that all it takes is me manually doing "sudo service nut-server restart” is all it takes. Clients connect and everything. Thanks, Todd -- Todd Benivegna // todd at benivegna.com On Aug 11, 2020, 10:29 PM -0400, Todd Benivegna <todd at benivegna.com>, wrote:> Thanks Manuel. I’m following that guide but am now stuck when checking to make sure the nut-sever and nut-client are up and working. I got this: > > proton at proton:~$ service nut-server status > nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) > Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 18s ago > Process: 1537 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) > > Warning: some journal files were not opened due to insufficient permissions. > > > > proton at proton:~$ service nut-client status > nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller > Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; vendor preset: enabled) > Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 50s ago > Process: 1543 ExecStart=/sbin/upsmon (code=exited, status=1/FAILURE) > > Warning: some journal files were not opened due to insufficient permissions. > > > > Do I have incorrect permission on the conf files? I did change this a while back. Why should the default permissions be on the nut folder and the files in the nut folder? I changed from 555 to 640 I believe. > > proton at proton:~$ sudo ls -la /etc/nut > total 60 > drw-r----- 2 root nut 4096 Aug 11 22:13 . > drwxr-xr-x 147 root root 12288 Aug 11 22:02 .. > -rw-r----- 1 root nut 1543 Aug 11 22:13 nut.conf > -rw-r----- 1 root nut 5615 Aug 11 21:59 ups.conf > -rw-r----- 1 root nut 4601 Aug 11 22:04 upsd.conf > -rw-r----- 1 root nut 2466 Aug 11 22:09 upsd.users > -rw-r----- 1 root nut 15479 Aug 11 22:12 upsmon.conf > -rw-r----- 1 root nut 3879 Feb 8 2020 upssched.conf > > -- > Todd Benivegna // todd at benivegna.com > On Aug 11, 2020, 9:09 PM -0400, Manuel Wolfshant <wolfy at nobugconsulting.ro>, wrote: > > On 8/12/20 3:55 AM, Todd Benivegna wrote: > > > Manuel, > > > > > > You are absolutely right. I think this is all the Synology just being > > > very dumb. I guess those are my only two options at this point. > > > > > > I have no idea on how to set up the NUT server though on one of my > > > NUCs or my Pi. Do you know any good guides out there? > > > > there are literally tons of guides. for instance: > > > > https://www.reddit.com/r/homelab/comments/5ssb5h/ups_server_on_raspberry_pi/ > > and scroll down to configuring, past the apt install step (which you > > already did ) > > > > basically all you need is to edit a few files below /etc/nut/ . takes 5 > > min top > > > > > > > I’m guessing it’s easy enough to edit upsmon.conf on the Synology in > > > order to get that to become a slave; I think would be all that’s > > > required for the Synology NAS. > > > > > > > Yeah I saw that. Makes no sense. I can Wireshark it, however even if > > > I find the cause, I’d still have to go to Synology for resolution, > > > which I doubt will ever get fixed. Even if they do, I doubt it’d be > > > any time soon. Maybe that’s me being pessimistic, I don’t know, but I > > > just don’t if I have the time or energy for all that! > > > > > no need to wireshark any more, we already know that it sends bogus FSD > > > > > > > > _______________________________________________ > > Nut-upsuser mailing list > > Nut-upsuser at alioth-lists.debian.net > > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser-------------- next part -------------- An HTML attachment was scrubbed... URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200812/df30c4b2/attachment-0001.html>
Tim Dawson
2020-Aug-12  05:10 UTC
[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
For directory permissions, the "x" priv determines if you can access the directory, so going from 555 (r-x,r-x,r-x) to 640 (rw-,r--,---) pretty much locks out access to the dir. Myself, I'd go back to 555. 640 essentially locks the group "nut" out . . . - Tim On August 11, 2020 11:11:22 PM CDT, Todd Benivegna <todd at benivegna.com> wrote:>Ok, so just a follow-up to my last email; still following that guide, which is great…. Just stuck on getting the nut-server service starting automatically. Got everything else working. I’ve been able to get the nut-client starting up automatically at boot up (I had a missing “1” in upsmon.conf. Oooops!) However, I cannot get nut-server service to start-up automatically still. > >proton at proton:~$ service nut-server status >nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) > Active: failed (Result: exit-code) since Tue 2020-08-11 23:43:55 EDT; 2min 0s ago > Process: 1559 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) > > >proton at proton:~$ service nut-client status >nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller > Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; vendor preset: enabled) > Active: active (running) since Tue 2020-08-11 23:43:55 EDT; 2min 7s ago > Process: 1567 ExecStart=/sbin/upsmon (code=exited, status=0/SUCCESS) > Main PID: 1570 (upsmon) > Tasks: 2 (limit: 9019) > CGroup: /system.slice/nut-monitor.service >1569 /lib/nut/upsmon >1570 /lib/nut/upsmon >Warning: some journal files were not opened due to insufficient permissions. > > >I can get it to start manually by doing "sudo service nut-server restart". Then it starts up…. Just starts up and all is good. > > >proton at proton:~$ sudo service nut-server status >nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) > Active: active (running) since Tue 2020-08-11 23:49:50 EDT; 12s ago > Process: 2949 ExecStart=/sbin/upsd (code=exited, status=0/SUCCESS) > Main PID: 2950 (upsd) > Tasks: 1 (limit: 9019) > CGroup: /system.slice/nut-server.service >2950 /lib/nut/upsd >Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 >Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 >Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups >Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups >Aug 11 23:49:50 proton upsd[2950]: Startup successful >Aug 11 23:49:50 proton systemd[1]: Started Network UPS Tools - power devices information server. >Aug 11 23:49:50 proton upsd[2950]: User upsmon_local at 127.0.0.1 logged into UPS [ups] >Aug 11 23:49:51 proton upsd[2950]: User monuser at 192.168.1.70 logged into UPS [ups] >Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.30 logged into UPS [ups] >Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.20 logged into UPS [ups] > > > >Here is my upsd.conf: > >LISTEN 127.0.0.1 3493 >LISTEN 192.168.1.31 3493 > > > >Could it be a permissions issue? Weird that all it takes is me manually doing "sudo service nut-server restart” is all it takes. Clients connect and everything. > >Thanks, > >Todd > >-- >Todd Benivegna // todd at benivegna.com >On Aug 11, 2020, 10:29 PM -0400, Todd Benivegna <todd at benivegna.com>, wrote: >> Thanks Manuel. I’m following that guide but am now stuck when checking to make sure the nut-sever and nut-client are up and working. I got this: >> >> proton at proton:~$ service nut-server status >> nut-server.service - Network UPS Tools - power devices information server >> Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; vendor preset: enabled) >> Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 18s ago >> Process: 1537 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) >> >> Warning: some journal files were not opened due to insufficient permissions. >> >> >> >> proton at proton:~$ service nut-client status >> nut-monitor.service - Network UPS Tools - power device monitor and shutdown controller >> Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; vendor preset: enabled) >> Active: failed (Result: exit-code) since Tue 2020-08-11 22:13:42 EDT; 1min 50s ago >> Process: 1543 ExecStart=/sbin/upsmon (code=exited, status=1/FAILURE) >> >> Warning: some journal files were not opened due to insufficient permissions. >> >> >> >> Do I have incorrect permission on the conf files? I did change this a while back. Why should the default permissions be on the nut folder and the files in the nut folder? I changed from 555 to 640 I believe. >> >> proton at proton:~$ sudo ls -la /etc/nut >> total 60 >> drw-r----- 2 root nut 4096 Aug 11 22:13 . >> drwxr-xr-x 147 root root 12288 Aug 11 22:02 .. >> -rw-r----- 1 root nut 1543 Aug 11 22:13 nut.conf >> -rw-r----- 1 root nut 5615 Aug 11 21:59 ups.conf >> -rw-r----- 1 root nut 4601 Aug 11 22:04 upsd.conf >> -rw-r----- 1 root nut 2466 Aug 11 22:09 upsd.users >> -rw-r----- 1 root nut 15479 Aug 11 22:12 upsmon.conf >> -rw-r----- 1 root nut 3879 Feb 8 2020 upssched.conf >> >> -- >> Todd Benivegna // todd at benivegna.com >> On Aug 11, 2020, 9:09 PM -0400, Manuel Wolfshant <wolfy at nobugconsulting.ro>, wrote: >> > On 8/12/20 3:55 AM, Todd Benivegna wrote: >> > > Manuel, >> > > >> > > You are absolutely right. I think this is all the Synology just being >> > > very dumb. I guess those are my only two options at this point. >> > > >> > > I have no idea on how to set up the NUT server though on one of my >> > > NUCs or my Pi. Do you know any good guides out there? >> > >> > there are literally tons of guides. for instance: >> > >> > https://www.reddit.com/r/homelab/comments/5ssb5h/ups_server_on_raspberry_pi/ >> > and scroll down to configuring, past the apt install step (which you >> > already did ) >> > >> > basically all you need is to edit a few files below /etc/nut/ . takes 5 >> > min top >> > >> > >> > > I’m guessing it’s easy enough to edit upsmon.conf on the Synology in >> > > order to get that to become a slave; I think would be all that’s >> > > required for the Synology NAS. >> > >> > >> > > Yeah I saw that. Makes no sense. I can Wireshark it, however even if >> > > I find the cause, I’d still have to go to Synology for resolution, >> > > which I doubt will ever get fixed. Even if they do, I doubt it’d be >> > > any time soon. Maybe that’s me being pessimistic, I don’t know, but I >> > > just don’t if I have the time or energy for all that! >> > > >> > no need to wireshark any more, we already know that it sends bogus FSD >> > >> > >> > >> > _______________________________________________ >> > Nut-upsuser mailing list >> > Nut-upsuser at alioth-lists.debian.net >> > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser-- Sent from my Android device with K-9 Mail. Please excuse my brevity. -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20200812/7c8d304f/attachment-0003.html>
Manuel Wolfshant
2020-Aug-12  08:04 UTC
[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On 8/12/20 7:11 AM, Todd Benivegna wrote:> Ok, so just a follow-up to my last email; still following that guide, > which is great…. Just stuck on getting the nut-server service starting > automatically. Got everything else working. I’ve been able to get > the nut-client starting up automatically at boot up (I had a missing > “1” in upsmon.conf. Oooops!) However, I cannot get nut-server > service to start-up automatically still. > > proton at proton:~$ service nut-server status > nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; > vendor preset: enabled) > Active: failed (Result: exit-code) since Tue 2020-08-11 23:43:55 > EDT; 2min 0s ago > Process: 1559 ExecStart=/sbin/upsd (code=exited, status=1/FAILURE) > > > proton at proton:~$ service nut-client status > nut-monitor.service - Network UPS Tools - power device monitor and > shutdown controller > Loaded: loaded (/lib/systemd/system/nut-monitor.service; enabled; > vendor preset: enabled) > Active: active (running) since Tue 2020-08-11 23:43:55 EDT; 2min > 7s ago > Process: 1567 ExecStart=/sbin/upsmon (code=exited, status=0/SUCCESS) > Main PID: 1570 (upsmon) > Tasks: 2 (limit: 9019) > CGroup: /system.slice/nut-monitor.service > 1569 /lib/nut/upsmon > 1570 /lib/nut/upsmon > Warning: some journal files were not opened due to insufficient > permissions. > > > I can get it to start manually by doing "sudo service nut-server > restart". Then it starts up…. Just starts up and all is good. > > > proton at proton:~$ sudo service nut-server status > nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/lib/systemd/system/nut-server.service; enabled; > vendor preset: enabled) > Active: active (running) since Tue 2020-08-11 23:49:50 EDT; 12s ago > Process: 2949 ExecStart=/sbin/upsd (code=exited, status=0/SUCCESS) > Main PID: 2950 (upsd) > Tasks: 1 (limit: 9019) > CGroup: /system.slice/nut-server.service > 2950 /lib/nut/upsd > Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 > Aug 11 23:49:50 proton upsd[2949]: listening on 127.0.0.1 port 3493 > Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups > Aug 11 23:49:50 proton upsd[2949]: Connected to UPS [ups]: usbhid-ups-ups > Aug 11 23:49:50 proton upsd[2950]: Startup successful > Aug 11 23:49:50 proton systemd[1]: Started Network UPS Tools - power > devices information server. > Aug 11 23:49:50 proton upsd[2950]: User upsmon_local at 127.0.0.1 logged > into UPS [ups] > Aug 11 23:49:51 proton upsd[2950]: User monuser at 192.168.1.70 logged > into UPS [ups] > Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.30 > logged into UPS [ups] > Aug 11 23:49:53 proton upsd[2950]: User upsmon_remote at 192.168.1.20 > logged into UPS [ups] > > > > Here is my upsd.conf: > > LISTEN 127.0.0.1 3493 > LISTEN 192.168.1.31 3493 > > > > Could it be a permissions issue? Weird that all it takes is me > manually doing "sudo service nut-server restart” is all it > takes. Clients connect and everything.That is odd, indeed. And yes, it is certainly a permission issue but on the journal files which reside below /var/log , not on the config files Start with journactl -x as it might say more about the error. And maybe verify if any log file is defined by the nut-server unit. M.
Charles Lepple
2020-Aug-12  11:06 UTC
[Nut-upsuser] Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
On Aug 12, 2020, at 12:11 AM, Todd Benivegna <todd at benivegna.com> wrote:> > Here is my upsd.conf: > > LISTEN 127.0.0.1 3493 > LISTEN 192.168.1.31 3493 >Those LISTEN lines were appropriate pre-systemd when NUT's startup script was launched after networking was fully enabled. I would recommend "LISTEN 0.0.0.0 3493" instead, and use firewall rules if you are trying to exclude an interface (which is likely not the case on a Pi).
Possibly Parallel Threads
- Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
 - Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
 - Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
 - Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)
 - Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)