Arjen de Korte
2007-Jan-29 15:23 UTC
Antwort: Re: [Nut-upsuser] "no longer stale" when disconnected with 2.0.5
> here the output of "upsd -DDDDD" when starting "upsc apc@localhost > ups.status" (and stopping after 20-30 sec with an ctrl+c)Ah, you have a problem with 'upsc' rather than with 'upscmd' like you stated before. That changes things.> Connection from 127.0.0.1 > acl_check: localhost: match 1 > ACL [localhost] matches, action=1 > write: [destfd=6] [len=24] [VAR apc ups.status "OL"]This looks (almost) good, apparently upsd got a request to send the value of 'ups.status' and decoded this properly. It sends [VAR apc ups.status "OL"] in return, which looks good at first glance. But it isn't... ;-) Yesterday I committed a change to upsd.c to remove the trailing '\n' in debug mode, since that would break the line with 'write: ...' on it, which looked rather ugly. Bummer, since the rtrim() function that I used will strip it from the answer sent to the connecting client also, the answer will now be shorter than expected and miss the trailing '\n' (server/upsd.c): int sendback(ctype *client, const char *fmt, ...) [...] upsdebugx(2, "write: [destfd=%d] [len=%d] [%s]", client->fd, len, rtrim(ans, '\n')); if (client->ssl) res = ssl_write(client, ans, len); else res = write(client->fd, ans, len); The solution is to move the line with upsdebugx to after the lines writing this to the client. I will commit this fix later today. This is an unrelated problem from the staleness warnings though. Best regards, Arjen