Oops, sorry about missing your test two. I did not read it all the way
through.
That test is done, and nut-server starts successfully. Upsc will give
back information about the device. I did have to run a daemon-reload.
It does complain about not finding the PID file.
================================[root at mythtv ups]# cat
/etc/systemd/system/nut-server.service.d/environ.conf
[Service]
Environment=NUT_STATEPATH=/run/nut
[root at mythtv ups]# cat
/etc/systemd/system/nut-driver at .service.d/environ.conf
[Service]
Environment=NUT_STATEPATH=/run/nut
[root at mythtv ups]# systemctl --full --no-pager status nut-server
? nut-server.service - Network UPS Tools - power devices information server
Loaded: loaded (/usr/lib/systemd/system/nut-server.service;
enabled; preset: disabled)
Drop-In: /etc/systemd/system/nut-server.service.d
??environ.conf
Active: active (running) since Fri 2022-12-02 10:11:18 CST; 9s ago
Main PID: 12675 (upsd)
Tasks: 1 (limit: 9482)
Memory: 732.0K
CPU: 5ms
CGroup: /system.slice/nut-server.service
??12675 /usr/sbin/upsd -F
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen
/run/nut/upsd.pid: No such file or directory
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find
PID file '/run/nut/upsd.pid' to see if previous upsd instance is already
running!
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on ::1
port 3493
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on
127.0.0.1 port 3493
Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on ::1 port 3493
Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on 127.0.0.1
port 3493
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Connected to UPS
[cyberpower]: usbhid-ups-cyberpower
Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Connected to UPS
[cyberpower]: usbhid-ups-cyberpower
Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Running as foreground
process, not saving a PID file
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Running as
foreground process, not saving a PID file
============================
==============Bill Gee
On 12/2/22 06:24, Simon Wilson via Nut-upsuser wrote:> Hi Bill,
>
> OK your test 1 and 2 line up with my ask for test 1 :)
>
> Have another read of the Test 2 ask please if you can:
>
>>> 2. Second test:- copy the edited
>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to
>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you
should
>>> at that point have both locations with a file saying
>>> ? [Service]
>>> ? Environment=NUT_STATEPATH=/run/nut
>>> Then comment out STATEPATH line (back to default) in upsd.conf and
>>> restart nut-server - does it still start, and does it still pop a
>>> "Could not find PID file '/var/run/upsd.pid'"
message? That tests
>>> whether the drop-in file is a better, more consistent fix for now
>>> (until the packages are resolved). Calling the nut-server process
>>> with that variable set for upsd *even before it reads upsd.conf*
may
>>> remove the first error 'Could not find PID file
'/var/run/upsd.pid''
>
> Your test 3 and 4 are not quite what is needed, unless you did copy the
> environ.conf file into /etc/systemd/system/nut-server.service.d/ but
> didn't say so?
>
> Could you please copy your nut-driver's environ.conf file to
> /etc/systemd/system/nut-server.service.d/ THEN comment out the STATEPATH
> line and see if nut-server starts.
>
> Why am I asking this>
> At the moment you are using one fix to resolve the driver (an
> environ.conf file) and a different fix to get nut-server going
> (STATEPATH). Trying to see if one fix (the environ.conf file fix) will
> resolve both driver and server, and in doing so also get rid of the
> error message 'Could not find PID file
'/var/run/upsd.pid''.
>
> Simon
>
> ----- Message from Bill Gee <bgee at campercaver.net> ---------
> ?? Date: Fri, 2 Dec 2022 06:07:20 -0600
> ?? From: Bill Gee <bgee at campercaver.net>
> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
> ???? To: nut-upsuser at alioth-lists.debian.net
>
>
>> Test 1 - I moved the environ.conf file to /tmp.? I ran systemctl
>> daemon-reload, then restarted nut-driver at cyberpower.service.?
Results:
>>
>> ====================================>> [root at mythtv nut-driver
at .service.d]# systemctl restart
>> nut-driver at cyberpower.service
>> Job for nut-driver at cyberpower.service failed because the control
>> process exited with error code.
>> See "systemctl status nut-driver at cyberpower.service" and
"journalctl
>> -xeu nut-driver at cyberpower.service" for details.
>> [root at mythtv nut-driver at .service.d]# systemctl --full --no-pager
>> status nut-driver at cyberpower.service
>> ? nut-driver at cyberpower.service - Network UPS Tools - device driver
>> for NUT device 'cyberpower'
>> ???? Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service;
>> enabled; preset: disabled)
>> ??? Drop-In: /etc/systemd/system/nut-driver at cyberpower.service.d
>> ???????????? ??nut-driver-enumerator-generated-checksum.conf,
>> nut-driver-enumerator-generated.conf
>> ???? Active: activating (auto-restart) (Result: exit-code) since Fri
>> 2022-12-02 05:54:03 CST; 2s ago
>> ??? Process: 10732 ExecStartPre=/usr/bin/systemd-tmpfiles --create
>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, status=0/SUCCESS)
>> ??? Process: 10733 ExecStart=/bin/sh -c
>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh
>> --get-device-for-service cyberpower`" && [ -n
"$NUTDEV" ] || { echo
>> "FATAL: Could not find a NUT device section for service unit
>> cyberpower" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start
"$NUTDEV"
>> (code=exited, status=1/FAILURE)
>> ??????? CPU: 80ms
>> ========================================>>
>> It seems that the nut device driver requires environ.conf to be
present.
>>
>> Test 2 - I moved environ.conf back to the correct place.? I edited the
>> file to use "Environment=NUT_STATEPATH=/run/nut".? I did a
>> daemon-reload then started the nut-driver.? It worked - no errors.
>>
>> Test 3 - I modified /etc/ups/upsd.conf to comment out the STATEPATH
>> line.? I restarted nut-server.service.? It failed.
>>
>> ===============================>> [root at mythtv ups]# systemctl
--full --no-pager status nut-server
>> ? nut-server.service - Network UPS Tools - power devices information
>> server
>> ???? Loaded: loaded (/usr/lib/systemd/system/nut-server.service;
>> enabled; preset: disabled)
>> ???? Active: active (running) since Fri 2022-12-02 06:00:54 CST; 13s
ago
>> ?? Main PID: 11452 (upsd)
>> ????? Tasks: 1 (limit: 9482)
>> ???? Memory: 728.0K
>> ??????? CPU: 5ms
>> ???? CGroup: /system.slice/nut-server.service
>> ???????????? ??11452 /usr/sbin/upsd -F
>>
>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on
>> ::1 port 3493
>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on
>> 127.0.0.1 port 3493
>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on ::1
>> port 3493
>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on
>> 127.0.0.1 port 3493
>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: /var/run is
>> world readable
>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: /var/run is world
>> readable
>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Can't connect to
UPS
>> [cyberpower] (usbhid-ups-cyberpower): No such file or directory
>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Can't
connect
>> to UPS [cyberpower] (usbhid-ups-cyberpower): No such file or directory
>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Running as
>> foreground process, not saving a PID file
>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Running as
>> foreground process, not saving a PID file
>> ==================================>>
>> Test 4 - I uncommented the STATEPATH line in upsd.conf.? It points to
>> /run/nut.? I restarted nut-server.? Success.
>>
>>
>> ==============>> Bill Gee
>>
>> On 12/1/22 18:35, Simon Wilson via Nut-upsuser wrote:
>>> Resending as original was too big for list acceptance.
>>>
>>> Hi Bill,
>>>
>>> /etc/systemd/system/nut-driver at .service.d/environ.conf sets the
>>> nut-driver service's environment variable, such that it sees a
>>> workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by the
>>> service, regardless of what is set in upsd.conf, and explains why
the
>>> driver worked yesterday but upsd didn't.
>>>
>>> Tests which may be interesting:
>>>
>>> 1. First test:- move nut-driver's environ.conf file to
somewhere else
>>> temporarily; leave upsd.conf STATEPATH uncommented saying /run/nut;
>>> restart nut-driver at cyberpower.service; and see if it runs. This
tests
>>> to see if it *needs* the drop-in service file *or* will work with
>>> only STATEPATH explicitly set in upsd.conf to /run/nut.? If this
>>> prevents the driver from working, put the environ.conf file back
(but
>>> edit it, it should say /run/nut, not /var/run/nut)
>>>
>>> 2. Second test:- copy the edited
>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to
>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you
should
>>> at that point have both locations with a file saying
>>> ? [Service]
>>> ? Environment=NUT_STATEPATH=/run/nut
>>> Then comment out STATEPATH line (back to default) in upsd.conf and
>>> restart nut-server - does it still start, and does it still pop a
>>> "Could not find PID file '/var/run/upsd.pid'"
message? That tests
>>> whether the drop-in file is a better, more consistent fix for now
>>> (until the packages are resolved). Calling the nut-server process
>>> with that variable set for upsd *even before it reads upsd.conf*
may
>>> remove the first error 'Could not find PID file
'/var/run/upsd.pid''
>>>
>>> And definitely document any changes you make to your setup as
>>> subsequent package releases will likely change all of this :)
>>>
>>> Couple more comments inline below.
>>>
>>> Simon
>>>
>>>
>>> ----- Message from Bill Gee <bgee at campercaver.net>
---------
>>> ? ?Date: Thu, 1 Dec 2022 16:49:14 -0600
>>> ? ?From: Bill Gee <bgee at campercaver.net>
>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8
upgrade
>>> ? ? ?To: nut-upsuser at alioth-lists.debian.net
>>>
>>>> Checking now - There is a file called
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf.? Its
>>>> contents are
>>>>
>>>> =========================>>>> [root at mythtv
nut-driver at .service.d]# ll
>>>> total 8
>>>> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf
>>>> -rw-r--r-- 1 root root 81 Nov 30 18:58
>>>> nut-driver-enumerator-generated-checksum.conf
>>>>
>>>> [root at mythtv nut-driver at .service.d]# cat environ.conf
>>>> [Service]
>>
>> [snip]
>>
>> _______________________________________________
>> Nut-upsuser mailing list
>> Nut-upsuser at alioth-lists.debian.net
>> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
>
> ----- End message from Bill Gee <bgee at campercaver.net> -----
>
>
>
Jim Klimov
2022-Dec-02 22:24 UTC
[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
FWIW, this and other recent discussions led to a few PRs and investigative issues about paths and PIDs and signals - so here's some reading for your enjoyment: * https://github.com/networkupstools/nut/pull/1724 * https://github.com/networkupstools/nut/issues/1721 * https://github.com/networkupstools/nut/issues/1728 * https://github.com/networkupstools/nut/issues/1727 * https://github.com/networkupstools/nut/pull/1719 * https://github.com/networkupstools/nut/issues/1712 * https://github.com/networkupstools/nut/issues/1714 Jim On Fri, Dec 2, 2022, 17:19 Bill Gee <bgee at campercaver.net> wrote:> Oops, sorry about missing your test two. I did not read it all the way > through. > > That test is done, and nut-server starts successfully. Upsc will give > back information about the device. I did have to run a daemon-reload. > It does complain about not finding the PID file. > > ================================> [root at mythtv ups]# cat > /etc/systemd/system/nut-server.service.d/environ.conf > [Service] > Environment=NUT_STATEPATH=/run/nut > [root at mythtv ups]# cat > /etc/systemd/system/nut-driver at .service.d/environ.conf > [Service] > Environment=NUT_STATEPATH=/run/nut > > [root at mythtv ups]# systemctl --full --no-pager status nut-server > ? nut-server.service - Network UPS Tools - power devices information server > Loaded: loaded (/usr/lib/systemd/system/nut-server.service; > enabled; preset: disabled) > Drop-In: /etc/systemd/system/nut-server.service.d > ??environ.conf > Active: active (running) since Fri 2022-12-02 10:11:18 CST; 9s ago > Main PID: 12675 (upsd) > Tasks: 1 (limit: 9482) > Memory: 732.0K > CPU: 5ms > CGroup: /system.slice/nut-server.service > ??12675 /usr/sbin/upsd -F > > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen > /run/nut/upsd.pid: No such file or directory > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find > PID file '/run/nut/upsd.pid' to see if previous upsd instance is already > running! > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on ::1 > port 3493 > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on > 127.0.0.1 port 3493 > Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on ::1 port > 3493 > Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on 127.0.0.1 > port 3493 > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Connected to UPS > [cyberpower]: usbhid-ups-cyberpower > Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Connected to UPS > [cyberpower]: usbhid-ups-cyberpower > Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Running as foreground > process, not saving a PID file > Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Running as > foreground process, not saving a PID file > ============================> > ==============> Bill Gee > > On 12/2/22 06:24, Simon Wilson via Nut-upsuser wrote: > > Hi Bill, > > > > OK your test 1 and 2 line up with my ask for test 1 :) > > > > Have another read of the Test 2 ask please if you can: > > > >>> 2. Second test:- copy the edited > >>> /etc/systemd/system/nut-driver at .service.d/environ.conf to > >>> /etc/systemd/system/nut-server.service.d/environ.conf. So you should > >>> at that point have both locations with a file saying > >>> [Service] > >>> Environment=NUT_STATEPATH=/run/nut > >>> Then comment out STATEPATH line (back to default) in upsd.conf and > >>> restart nut-server - does it still start, and does it still pop a > >>> "Could not find PID file '/var/run/upsd.pid'" message? That tests > >>> whether the drop-in file is a better, more consistent fix for now > >>> (until the packages are resolved). Calling the nut-server process > >>> with that variable set for upsd *even before it reads upsd.conf* may > >>> remove the first error 'Could not find PID file '/var/run/upsd.pid'' > > > > Your test 3 and 4 are not quite what is needed, unless you did copy the > > environ.conf file into /etc/systemd/system/nut-server.service.d/ but > > didn't say so? > > > > Could you please copy your nut-driver's environ.conf file to > > /etc/systemd/system/nut-server.service.d/ THEN comment out the STATEPATH > > line and see if nut-server starts. > > > > Why am I asking this> > > At the moment you are using one fix to resolve the driver (an > > environ.conf file) and a different fix to get nut-server going > > (STATEPATH). Trying to see if one fix (the environ.conf file fix) will > > resolve both driver and server, and in doing so also get rid of the > > error message 'Could not find PID file '/var/run/upsd.pid''. > > > > Simon > > > > ----- Message from Bill Gee <bgee at campercaver.net> --------- > > Date: Fri, 2 Dec 2022 06:07:20 -0600 > > From: Bill Gee <bgee at campercaver.net> > > Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade > > To: nut-upsuser at alioth-lists.debian.net > > > > > >> Test 1 - I moved the environ.conf file to /tmp. I ran systemctl > >> daemon-reload, then restarted nut-driver at cyberpower.service. Results: > >> > >> ====================================> >> [root at mythtv nut-driver at .service.d]# systemctl restart > >> nut-driver at cyberpower.service > >> Job for nut-driver at cyberpower.service failed because the control > >> process exited with error code. > >> See "systemctl status nut-driver at cyberpower.service" and "journalctl > >> -xeu nut-driver at cyberpower.service" for details. > >> [root at mythtv nut-driver at .service.d]# systemctl --full --no-pager > >> status nut-driver at cyberpower.service > >> ? nut-driver at cyberpower.service - Network UPS Tools - device driver > >> for NUT device 'cyberpower' > >> Loaded: loaded (/usr/lib/systemd/system/nut-driver at .service; > >> enabled; preset: disabled) > >> Drop-In: /etc/systemd/system/nut-driver at cyberpower.service.d > >> ??nut-driver-enumerator-generated-checksum.conf, > >> nut-driver-enumerator-generated.conf > >> Active: activating (auto-restart) (Result: exit-code) since Fri > >> 2022-12-02 05:54:03 CST; 2s ago > >> Process: 10732 ExecStartPre=/usr/bin/systemd-tmpfiles --create > >> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, status=0/SUCCESS) > >> Process: 10733 ExecStart=/bin/sh -c > >> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh > >> --get-device-for-service cyberpower`" && [ -n "$NUTDEV" ] || { echo > >> "FATAL: Could not find a NUT device section for service unit > >> cyberpower" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl start "$NUTDEV" > >> (code=exited, status=1/FAILURE) > >> CPU: 80ms > >> ========================================> >> > >> It seems that the nut device driver requires environ.conf to be present. > >> > >> Test 2 - I moved environ.conf back to the correct place. I edited the > >> file to use "Environment=NUT_STATEPATH=/run/nut". I did a > >> daemon-reload then started the nut-driver. It worked - no errors. > >> > >> Test 3 - I modified /etc/ups/upsd.conf to comment out the STATEPATH > >> line. I restarted nut-server.service. It failed. > >> > >> ===============================> >> [root at mythtv ups]# systemctl --full --no-pager status nut-server > >> ? nut-server.service - Network UPS Tools - power devices information > >> server > >> Loaded: loaded (/usr/lib/systemd/system/nut-server.service; > >> enabled; preset: disabled) > >> Active: active (running) since Fri 2022-12-02 06:00:54 CST; 13s ago > >> Main PID: 11452 (upsd) > >> Tasks: 1 (limit: 9482) > >> Memory: 728.0K > >> CPU: 5ms > >> CGroup: /system.slice/nut-server.service > >> ??11452 /usr/sbin/upsd -F > >> > >> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on > >> ::1 port 3493 > >> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening on > >> 127.0.0.1 port 3493 > >> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on ::1 > >> port 3493 > >> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on > >> 127.0.0.1 port 3493 > >> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: /var/run is > >> world readable > >> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: /var/run is world > >> readable > >> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Can't connect to UPS > >> [cyberpower] (usbhid-ups-cyberpower): No such file or directory > >> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Can't connect > >> to UPS [cyberpower] (usbhid-ups-cyberpower): No such file or directory > >> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Running as > >> foreground process, not saving a PID file > >> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Running as > >> foreground process, not saving a PID file > >> ==================================> >> > >> Test 4 - I uncommented the STATEPATH line in upsd.conf. It points to > >> /run/nut. I restarted nut-server. Success. > >> > >> > >> ==============> >> Bill Gee > >> > >> On 12/1/22 18:35, Simon Wilson via Nut-upsuser wrote: > >>> Resending as original was too big for list acceptance. > >>> > >>> Hi Bill, > >>> > >>> /etc/systemd/system/nut-driver at .service.d/environ.conf sets the > >>> nut-driver service's environment variable, such that it sees a > >>> workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by the > >>> service, regardless of what is set in upsd.conf, and explains why the > >>> driver worked yesterday but upsd didn't. > >>> > >>> Tests which may be interesting: > >>> > >>> 1. First test:- move nut-driver's environ.conf file to somewhere else > >>> temporarily; leave upsd.conf STATEPATH uncommented saying /run/nut; > >>> restart nut-driver at cyberpower.service; and see if it runs. This tests > >>> to see if it *needs* the drop-in service file *or* will work with > >>> only STATEPATH explicitly set in upsd.conf to /run/nut. If this > >>> prevents the driver from working, put the environ.conf file back (but > >>> edit it, it should say /run/nut, not /var/run/nut) > >>> > >>> 2. Second test:- copy the edited > >>> /etc/systemd/system/nut-driver at .service.d/environ.conf to > >>> /etc/systemd/system/nut-server.service.d/environ.conf. So you should > >>> at that point have both locations with a file saying > >>> [Service] > >>> Environment=NUT_STATEPATH=/run/nut > >>> Then comment out STATEPATH line (back to default) in upsd.conf and > >>> restart nut-server - does it still start, and does it still pop a > >>> "Could not find PID file '/var/run/upsd.pid'" message? That tests > >>> whether the drop-in file is a better, more consistent fix for now > >>> (until the packages are resolved). Calling the nut-server process > >>> with that variable set for upsd *even before it reads upsd.conf* may > >>> remove the first error 'Could not find PID file '/var/run/upsd.pid'' > >>> > >>> And definitely document any changes you make to your setup as > >>> subsequent package releases will likely change all of this :) > >>> > >>> Couple more comments inline below. > >>> > >>> Simon > >>> > >>> > >>> ----- Message from Bill Gee <bgee at campercaver.net> --------- > >>> Date: Thu, 1 Dec 2022 16:49:14 -0600 > >>> From: Bill Gee <bgee at campercaver.net> > >>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade > >>> To: nut-upsuser at alioth-lists.debian.net > >>> > >>>> Checking now - There is a file called > >>>> /etc/systemd/system/nut-driver at .service.d/environ.conf. Its > >>>> contents are > >>>> > >>>> =========================> >>>> [root at mythtv nut-driver at .service.d]# ll > >>>> total 8 > >>>> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf > >>>> -rw-r--r-- 1 root root 81 Nov 30 18:58 > >>>> nut-driver-enumerator-generated-checksum.conf > >>>> > >>>> [root at mythtv nut-driver at .service.d]# cat environ.conf > >>>> [Service] > >> > >> [snip] > >> > >> _______________________________________________ > >> Nut-upsuser mailing list > >> Nut-upsuser at alioth-lists.debian.net > >> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser > > > > > > ----- End message from Bill Gee <bgee at campercaver.net> ----- > > > > > > > > _______________________________________________ > Nut-upsuser mailing list > Nut-upsuser at alioth-lists.debian.net > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser >-------------- next part -------------- An HTML attachment was scrubbed... URL: <http://alioth-lists.debian.net/pipermail/nut-upsuser/attachments/20221202/fbd9aaea/attachment-0001.htm>
Simon Wilson
2022-Dec-03 03:50 UTC
[Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
Aha!! Bingo, that resolved the issue for upsd. You may not have picked
iut up Bill but the new "error" message shows it.
Going back to your message from yesterday, upsd logged this:
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: fopen
/var/run/upsd.pid: No such file or directory
Dec 01 10:35:01 mythtv.billgee.local nut-server[3445]: Could not find
PID file '/var/run/upsd.pid' to see if previous upsd instance is
already running!
With an environ.conf setting NUT_STATEPATH upsd logged this:
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen
/run/nut/upsd.pid: No such file or directory
Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not find
PID file '/run/nut/upsd.pid' to see if previous upsd instance is
already running!
Note the difference - it is now looking in the CORRECT FOLDER
/run/nut! There is not a pid there, that is fine - that pid check is
to see if there is a upsd already running. Now it is pointing at a
folder that nut can write too, that should work as designed. Awesome...
So, I think I'm right in summarising as follows for Bill's situation:
On Fedora / RH packages for 2.8.0
* need to create a /usr/lib/tmpfiles.d/nut-client.conf which contains
"D /run/nut 0770 root nut - -" to ensure the path exists for services
which look for it (or edit the service files to point to
nut-common.conf - but my preference is not to edit service files
directly to prevent later breaks)
* nut-driver
-- setting/uncommenting STATEPATH in upsd.conf to /var/run/nut or
/run/nut as the *only* fix does NOT allow driver to start - it still
tries to go to /var/run (this one I am not 100% sure of from looking
back through the thread, but I *think* is correct)
-- can be fixed by dropping in a service.d/ drop-in file which sets
Environment=NUT_STATEPATH=/run/nut
* nut-server
-- setting STATEPATH in upsd.conf to /var/run/nut or /run/nut **does**
allow server to start (unlike the driver)
-- can also be fixed by dropping in a service.d/ drop-in file which
sets Environment=NUT_STATEPATH=/run/nut
-- the drop-in is a better fix than uncommenting/setting STATEPATH, as
it makes upsd look in the correct folder for all of its pid tests
Bill, have I summarised those correctly?
It would seem that using drop-in files to set NUT_STATEPATH for both
upsdrvctl (nut-driver) and upsd (nut-server) is probably the best
short-term fix.
What is curious is the variation between packages and OSs though.
- For Bill on F37 all the above fixes were needed - nut-client.conf,
and both nut-driver and nut-server needed fixing for STATEPATH, with
two x drop-in files.
- For me on RHEL8.7 (which comes with a working 2.7.4 btw, so I'm my
own worst enemy there), installing the available 2.8.0-1.el8 package
was broken, but I only needed to fix the nut-client.conf issue, I did
not need to uncomment STATEPATH in upsd.conf or add drop-in files to
set NUT_STATEPATH - and driver and server both start fine, looking in
/run/nut.
Bill, you should now have a fully working nut stack. I assume you have
configured users and got nut-monitor working?
Simon
----- Message from Bill Gee <bgee at campercaver.net> ---------
Date: Fri, 2 Dec 2022 10:19:20 -0600
From: Bill Gee <bgee at campercaver.net>
Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8 upgrade
To: nut-upsuser at alioth-lists.debian.net
> Oops, sorry about missing your test two. I did not read it all the
> way through.
>
> That test is done, and nut-server starts successfully. Upsc will
> give back information about the device. I did have to run a
> daemon-reload. It does complain about not finding the PID file.
>
> ================================> [root at mythtv ups]# cat
/etc/systemd/system/nut-server.service.d/environ.conf
> [Service]
> Environment=NUT_STATEPATH=/run/nut
> [root at mythtv ups]# cat /etc/systemd/system/nut-driver at
.service.d/environ.conf
> [Service]
> Environment=NUT_STATEPATH=/run/nut
>
> [root at mythtv ups]# systemctl --full --no-pager status nut-server
> ? nut-server.service - Network UPS Tools - power devices information server
> Loaded: loaded (/usr/lib/systemd/system/nut-server.service;
> enabled; preset: disabled)
> Drop-In: /etc/systemd/system/nut-server.service.d
> ??environ.conf
> Active: active (running) since Fri 2022-12-02 10:11:18 CST; 9s ago
> Main PID: 12675 (upsd)
> Tasks: 1 (limit: 9482)
> Memory: 732.0K
> CPU: 5ms
> CGroup: /system.slice/nut-server.service
> ??12675 /usr/sbin/upsd -F
>
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: fopen
> /run/nut/upsd.pid: No such file or directory
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Could not
> find PID file '/run/nut/upsd.pid' to see if previous upsd instance
> is already running!
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on
> ::1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: listening on
> 127.0.0.1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on ::1 port
3493
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: listening on
> 127.0.0.1 port 3493
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Connected to
> UPS [cyberpower]: usbhid-ups-cyberpower
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Connected to UPS
> [cyberpower]: usbhid-ups-cyberpower
> Dec 02 10:11:18 mythtv.billgee.local upsd[12675]: Running as
> foreground process, not saving a PID file
> Dec 02 10:11:18 mythtv.billgee.local nut-server[12675]: Running as
> foreground process, not saving a PID file
> ============================>
> ==============> Bill Gee
>
> On 12/2/22 06:24, Simon Wilson via Nut-upsuser wrote:
>> Hi Bill,
>>
>> OK your test 1 and 2 line up with my ask for test 1 :)
>>
>> Have another read of the Test 2 ask please if you can:
>>
>>>> 2. Second test:- copy the edited
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to
>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you
>>>> should at that point have both locations with a file saying
>>>> ? [Service]
>>>> ? Environment=NUT_STATEPATH=/run/nut
>>>> Then comment out STATEPATH line (back to default) in upsd.conf
>>>> and restart nut-server - does it still start, and does it still
>>>> pop a "Could not find PID file
'/var/run/upsd.pid'" message? That
>>>> tests whether the drop-in file is a better, more consistent fix
>>>> for now (until the packages are resolved). Calling the
nut-server
>>>> process with that variable set for upsd *even before it reads
>>>> upsd.conf* may remove the first error 'Could not find PID
file
>>>> '/var/run/upsd.pid''
>>
>> Your test 3 and 4 are not quite what is needed, unless you did copy
>> the environ.conf file into
>> /etc/systemd/system/nut-server.service.d/ but didn't say so?
>>
>> Could you please copy your nut-driver's environ.conf file to
>> /etc/systemd/system/nut-server.service.d/ THEN comment out the
>> STATEPATH line and see if nut-server starts.
>>
>> Why am I asking this>
>> At the moment you are using one fix to resolve the driver (an
>> environ.conf file) and a different fix to get nut-server going
>> (STATEPATH). Trying to see if one fix (the environ.conf file fix)
>> will resolve both driver and server, and in doing so also get rid
>> of the error message 'Could not find PID file
'/var/run/upsd.pid''.
>>
>> Simon
>>
>> ----- Message from Bill Gee <bgee at campercaver.net> ---------
>> ?? Date: Fri, 2 Dec 2022 06:07:20 -0600
>> ?? From: Bill Gee <bgee at campercaver.net>
>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 -> 2.8
upgrade
>> ???? To: nut-upsuser at alioth-lists.debian.net
>>
>>
>>> Test 1 - I moved the environ.conf file to /tmp.? I ran systemctl
>>> daemon-reload, then restarted nut-driver at cyberpower.service.?
>>> Results:
>>>
>>> ====================================>>> [root at mythtv
nut-driver at .service.d]# systemctl restart
>>> nut-driver at cyberpower.service
>>> Job for nut-driver at cyberpower.service failed because the control
>>> process exited with error code.
>>> See "systemctl status nut-driver at cyberpower.service"
and
>>> "journalctl -xeu nut-driver at cyberpower.service" for
details.
>>> [root at mythtv nut-driver at .service.d]# systemctl --full
--no-pager
>>> status nut-driver at cyberpower.service
>>> ? nut-driver at cyberpower.service - Network UPS Tools - device
>>> driver for NUT device 'cyberpower'
>>> ???? Loaded: loaded (/usr/lib/systemd/system/nut-driver at
.service;
>>> enabled; preset: disabled)
>>> ??? Drop-In: /etc/systemd/system/nut-driver at cyberpower.service.d
>>> ???????????? ??nut-driver-enumerator-generated-checksum.conf,
>>> nut-driver-enumerator-generated.conf
>>> ???? Active: activating (auto-restart) (Result: exit-code) since
>>> Fri 2022-12-02 05:54:03 CST; 2s ago
>>> ??? Process: 10732 ExecStartPre=/usr/bin/systemd-tmpfiles --create
>>> /usr/lib/tmpfiles.d/nut-client.conf (code=exited, status=0/SUCCESS)
>>> ??? Process: 10733 ExecStart=/bin/sh -c
>>> NUTDEV="`/usr/libexec/nut-driver-enumerator.sh
>>> --get-device-for-service cyberpower`" && [ -n
"$NUTDEV" ] || {
>>> echo "FATAL: Could not find a NUT device section for service
unit
>>> cyberpower" >&2 ; exit 1 ; } ; /usr/sbin/upsdrvctl
start "$NUTDEV"
>>> (code=exited, status=1/FAILURE)
>>> ??????? CPU: 80ms
>>> ========================================>>>
>>> It seems that the nut device driver requires environ.conf to be
present.
>>>
>>> Test 2 - I moved environ.conf back to the correct place.? I edited
>>> the file to use "Environment=NUT_STATEPATH=/run/nut".? I
did a
>>> daemon-reload then started the nut-driver.? It worked - no errors.
>>>
>>> Test 3 - I modified /etc/ups/upsd.conf to comment out the
>>> STATEPATH line.? I restarted nut-server.service.? It failed.
>>>
>>> ===============================>>> [root at mythtv ups]#
systemctl --full --no-pager status nut-server
>>> ? nut-server.service - Network UPS Tools - power devices
information server
>>> ???? Loaded: loaded (/usr/lib/systemd/system/nut-server.service;
>>> enabled; preset: disabled)
>>> ???? Active: active (running) since Fri 2022-12-02 06:00:54 CST;
13s ago
>>> ?? Main PID: 11452 (upsd)
>>> ????? Tasks: 1 (limit: 9482)
>>> ???? Memory: 728.0K
>>> ??????? CPU: 5ms
>>> ???? CGroup: /system.slice/nut-server.service
>>> ???????????? ??11452 /usr/sbin/upsd -F
>>>
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening
>>> on ::1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: listening
>>> on 127.0.0.1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on ::1
>>> port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: listening on
>>> 127.0.0.1 port 3493
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: /var/run
>>> is world readable
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: /var/run is
>>> world readable
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Can't connect
to
>>> UPS [cyberpower] (usbhid-ups-cyberpower): No such file or directory
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Can't
>>> connect to UPS [cyberpower] (usbhid-ups-cyberpower): No such file
>>> or directory
>>> Dec 02 06:00:54 mythtv.billgee.local nut-server[11452]: Running as
>>> foreground process, not saving a PID file
>>> Dec 02 06:00:54 mythtv.billgee.local upsd[11452]: Running as
>>> foreground process, not saving a PID file
>>> ==================================>>>
>>> Test 4 - I uncommented the STATEPATH line in upsd.conf.? It points
>>> to /run/nut.? I restarted nut-server.? Success.
>>>
>>>
>>> ==============>>> Bill Gee
>>>
>>> On 12/1/22 18:35, Simon Wilson via Nut-upsuser wrote:
>>>> Resending as original was too big for list acceptance.
>>>>
>>>> Hi Bill,
>>>>
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf sets
the
>>>> nut-driver service's environment variable, such that it
sees a
>>>> workable NUT_STATEPATH of /var/run/nut when upsdrvctl is run by
>>>> the service, regardless of what is set in upsd.conf, and
explains
>>>> why the driver worked yesterday but upsd didn't.
>>>>
>>>> Tests which may be interesting:
>>>>
>>>> 1. First test:- move nut-driver's environ.conf file to
somewhere
>>>> else temporarily; leave upsd.conf STATEPATH uncommented saying
>>>> /run/nut; restart nut-driver at cyberpower.service; and see if
it
>>>> runs. This tests to see if it *needs* the drop-in service file
>>>> *or* will work with only STATEPATH explicitly set in upsd.conf
to
>>>> /run/nut.? If this prevents the driver from working, put the
>>>> environ.conf file back (but edit it, it should say /run/nut,
not
>>>> /var/run/nut)
>>>>
>>>> 2. Second test:- copy the edited
>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf to
>>>> /etc/systemd/system/nut-server.service.d/environ.conf. So you
>>>> should at that point have both locations with a file saying
>>>> ? [Service]
>>>> ? Environment=NUT_STATEPATH=/run/nut
>>>> Then comment out STATEPATH line (back to default) in upsd.conf
>>>> and restart nut-server - does it still start, and does it still
>>>> pop a "Could not find PID file
'/var/run/upsd.pid'" message? That
>>>> tests whether the drop-in file is a better, more consistent fix
>>>> for now (until the packages are resolved). Calling the
nut-server
>>>> process with that variable set for upsd *even before it reads
>>>> upsd.conf* may remove the first error 'Could not find PID
file
>>>> '/var/run/upsd.pid''
>>>>
>>>> And definitely document any changes you make to your setup as
>>>> subsequent package releases will likely change all of this :)
>>>>
>>>> Couple more comments inline below.
>>>>
>>>> Simon
>>>>
>>>>
>>>> ----- Message from Bill Gee <bgee at campercaver.net>
---------
>>>> ? ?Date: Thu, 1 Dec 2022 16:49:14 -0600
>>>> ? ?From: Bill Gee <bgee at campercaver.net>
>>>> Subject: Re: [Nut-upsuser] NUT no longer works after 2.7 ->
2.8 upgrade
>>>> ? ? ?To: nut-upsuser at alioth-lists.debian.net
>>>>
>>>>> Checking now - There is a file called
>>>>> /etc/systemd/system/nut-driver at .service.d/environ.conf.?
Its
>>>>> contents are
>>>>>
>>>>> =========================>>>>> [root at
mythtv nut-driver at .service.d]# ll
>>>>> total 8
>>>>> -rw-r--r-- 1 root root 49 Nov 29 18:14 environ.conf
>>>>> -rw-r--r-- 1 root root 81 Nov 30 18:58
>>>>> nut-driver-enumerator-generated-checksum.conf
>>>>>
>>>>> [root at mythtv nut-driver at .service.d]# cat environ.conf
>>>>> [Service]
>>>
>>> [snip]
>>>
>>> _______________________________________________
>>> Nut-upsuser mailing list
>>> Nut-upsuser at alioth-lists.debian.net
>>>
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>>
>>
>> ----- End message from Bill Gee <bgee at campercaver.net> -----
>>
>>
>>
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser at alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
----- End message from Bill Gee <bgee at campercaver.net> -----
--
Simon Wilson
M: 0400 12 11 16