Vassilis Virvilis
2016-Sep-08 13:25 UTC
[Nut-upsuser] blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
[snip hex dump analysis]> > It is possible that the blazer_usb driver initialization has put the UPS > into a bad state. If you can schedule some downtime, you might want to try > usbhid-ups again after powering the UPS down completely and unplugging it > for a little while. (Often, a few seconds after the output is off and the > AC has been removed, you will hear relays disengage.)Ok I am new to UPS and I can say that I would have never thought of that. So: 1) Shutdown the PC 2) Shutdown the UPS - several minutes (I am writing this e-mail) 3) Try to find a cirquit breaker - found one. Lucky! 4) Power up the UPS 5) Power up the PC - it is configured to start the nut-server with usbhid-ups 6) It failed to deal with the UPS 7) service nut-server stop (checked with ps all nut services are gone) 7) #mv delme delme.orig (previous file) 8) #/lib/nut/usbhid-ups -DDD -x explore -a turbo-x 2>&1 | tee > delme 9) strip the timings for diffing # sed 's/ [0-9\.]*\t//g' < delme.orig > delme.orig.1 # sed 's/ [0-9\.]*\t//g' < delme > delme.1 10) diff # diff -ur delme.orig.1 delme.1 | colordiff | less -SR --- delme.orig.1 2016-09-08 16:15:57.222453200 +0300 +++ delme.1 2016-09-08 16:16:05.206556873 +0300 @@ -1,25 +1,47 @@ debug level is '3' upsdrv_initups... - Checking device (067B/2305) (008/006) + Checking device (1D6B/0002) (008/001) + - VendorID: 1d6b + - ProductID: 0002 + - Manufacturer: unknown + - Product: unknown + - Serial Number: unknown + - Bus: 008 + - Device release number: 0407 + Trying to match device + Device does not match - skipping + Checking device (1D6B/0002) (007/001) + - VendorID: 1d6b + - ProductID: 0002 + - Manufacturer: unknown + - Product: unknown + - Serial Number: unknown + - Bus: 007 + - Device release number: 0407 + Trying to match device + Device does not match - skipping + Checking device (067B/2305) (006/003) - VendorID: 067b - ProductID: 2305 - Manufacturer: unknown - Product: unknown - Serial Number: unknown - - Bus: 008 + - Bus: 006 - Device release number: 0202 Trying to match device Device does not match - skipping - Checking device (0001/0000) (008/002) + Checking device (0001/0000) (006/002) - VendorID: 0001 - ProductID: 0000 - Manufacturer: MEC - Product: MEC0002 - Serial Number: unknown - - Bus: 008 + - Bus: 006 - Device release number: 0100 Trying to match device Device matches + failed to claim USB device: could not claim interface 0: Device or resource busy + detached kernel driver from USB device... nut_usb_set_altinterface: skipped usb_set_altinterface(udev, 0) HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 70 02 **** device or resource busy? 11) retrying as root #/lib/nut/usbhid-ups -DDD -u root -x explore -a turbo-x 2>&1 | tee delme.root 12) stripping, diffing -- no diffs Here is the root run output 0.000000 debug level is '3' 0.000538 upsdrv_initups... 0.143639 Checking device (1D6B/0002) (008/001) 0.167674 - VendorID: 1d6b 0.167685 - ProductID: 0002 0.167688 - Manufacturer: Linux 4.7.0-1-amd64 ehci_hcd 0.167741 - Product: EHCI Host Controller 0.167749 - Serial Number: 0000:00:1d.7 0.167753 - Bus: 008 0.167802 - Device release number: 0407 0.167849 Trying to match device 0.167899 Device does not match - skipping 0.167976 Checking device (1D6B/0002) (007/001) 0.168131 - VendorID: 1d6b 0.168140 - ProductID: 0002 0.168186 - Manufacturer: Linux 4.7.0-1-amd64 ehci_hcd 0.168194 - Product: EHCI Host Controller 0.168278 - Serial Number: 0000:00:1a.7 0.168287 - Bus: 007 0.168330 - Device release number: 0407 0.168338 Trying to match device 0.168345 Device does not match - skipping 0.179609 Checking device (067B/2305) (006/003) 0.188178 - VendorID: 067b 0.188188 - ProductID: 2305 0.188192 - Manufacturer: Prolific Technology Inc. 0.188251 - Product: IEEE-1284 Controller 0.188301 - Serial Number: unknown 0.188310 - Bus: 006 0.188358 - Device release number: 0202 0.188366 Trying to match device 0.188432 Device does not match - skipping 0.188488 Checking device (0001/0000) (006/002) 0.211178 - VendorID: 0001 0.211187 - ProductID: 0000 0.211191 - Manufacturer: MEC 0.211252 - Product: MEC0002 0.211301 - Serial Number: unknown 0.211310 - Bus: 006 0.211357 - Device release number: 0100 0.211365 Trying to match device 0.211439 Device matches 0.211509 nut_usb_set_altinterface: skipped usb_set_altinterface(udev, 0) 0.216183 HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 70 02 0.216193 HID descriptor length (method 1) 624 0.216250 HID descriptor, method 2: (9 bytes) => 09 21 00 01 00 01 22 70 02 0.216259 HID descriptor length (method 2) 624 0.216262 HID descriptor length 624 0.297182 Report Descriptor size = 624 0.297196 Report Descriptor: (624 bytes) => 05 86 09 04 a1 01 05 84 09 1e a1 00 85 01 0.297299 09 1f 65 00 75 04 95 01 15 00 25 0f 65 00 b1 02 75 04 95 01 b1 03 09 40 75 0.297354 10 95 01 67 21 d1 f0 00 55 07 15 00 26 fa 00 b1 02 09 42 75 10 95 01 66 01 0.297408 f0 55 00 15 00 25 3c b1 02 09 53 75 10 95 01 67 21 d1 f0 00 55 07 15 00 26 0.297463 fa 00 b1 02 09 54 75 10 95 01 67 21 d1 f0 00 55 07 15 00 26 fa 00 b1 02 09 0.297530 fd 09 fe 09 ff 75 08 95 03 26 ff 00 65 00 b1 00 c0 05 84 09 1e a1 00 85 02 0.297585 09 1f 65 00 75 04 95 01 15 00 25 0f 65 00 b1 02 95 01 75 04 b1 03 09 40 75 0.297640 10 95 01 67 21 d1 f0 00 55 07 15 00 26 fa 00 b1 02 09 42 75 10 95 01 66 01 0.297705 f0 55 00 15 00 25 3c b1 02 09 43 75 10 95 01 66 21 d1 55 07 15 00 27 fe ff 0.297760 00 00 b1 02 09 44 95 01 75 10 66 21 d1 55 07 15 00 27 fe ff 00 00 b1 02 09 0.297815 56 75 18 95 01 66 01 10 55 00 15 00 27 fe ff 00 00 b1 02 09 57 75 18 95 01 0.297870 66 01 10 55 00 15 00 27 fe ff 00 00 b1 02 c0 05 84 09 10 a1 00 85 03 09 11 0.297907 65 00 75 04 95 01 15 00 25 0f 65 00 b1 02 75 04 95 01 b1 03 09 02 a1 02 09 0.297917 6d 09 61 75 01 95 02 15 00 25 01 b1 02 75 06 95 01 b1 03 c0 09 30 75 18 95 0.297930 01 67 21 d1 f0 00 55 05 27 fe ff 00 00 b1 02 09 36 75 10 95 01 67 01 00 01 0.297939 00 27 fe ff 00 00 b1 02 09 58 75 01 95 06 15 00 25 01 81 02 75 02 95 01 81 0.297948 03 09 58 75 01 95 04 15 00 25 01 b1 02 75 04 95 01 b1 03 c0 05 84 09 16 a1 0.297957 00 85 04 09 17 75 04 95 01 15 00 25 0f 65 00 81 02 75 04 95 01 81 03 09 1a 0.297966 a1 00 09 1b 09 1f 75 04 95 02 15 00 25 0f 65 00 81 02 09 02 a1 02 09 61 75 0.297975 01 95 01 15 00 25 01 81 02 75 07 95 01 81 03 c0 09 30 75 10 95 01 67 21 d1 0.297983 f0 00 55 05 27 fe ff 00 00 81 02 09 32 75 10 95 01 66 01 f0 55 05 27 fe ff 0.297992 00 00 81 02 c0 09 1c a1 00 85 05 09 1d 09 1f 75 04 95 02 15 00 25 0f 65 00 0.298001 81 02 09 30 75 10 95 01 67 21 d1 f0 00 55 05 27 fe ff 00 00 81 02 09 32 75 0.298010 10 95 01 66 01 f0 55 05 27 fe ff 00 00 81 02 09 35 75 10 95 01 15 00 26 ff 0.298028 00 81 02 09 02 a1 02 09 65 09 6e 09 6f 75 01 95 03 15 00 25 01 65 00 81 02 0.298035 75 05 95 01 81 03 c0 c0 c0 c0 0.298098 Using subdriver: EXPLORE HID 0.1 0.298103 36 HID objects found 0.302190 refresh_report_buffer: expected 13 bytes, but got 8 instead 0.302204 Report[err]: (8 bytes) => 08 03 4d 00 45 00 43 00 0.302213 Path: 00860004.Flow.FlowID, Type: Feature, ReportID: 0x01, Offset: 0, Size: 4, Value: 3 0.302219 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302228 Path: 00860004.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 8, Size: 16, Value: 77 0.302234 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302245 Path: 00860004.Flow.ConfigFrequency, Type: Feature, ReportID: 0x01, Offset: 24, Size: 16, Value: 5 0.302252 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302259 Path: 00860004.Flow.LowVoltageTransfer, Type: Feature, ReportID: 0x01, Offset: 40, Size: 16, Value: 67 0.302266 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302281 Path: 00860004.Flow.HighVoltageTransfer, Type: Feature, ReportID: 0x01, Offset: 56, Size: 16, Value: 0 0.302287 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302292 Path: 00860004.Flow.iManufacturer, Type: Feature, ReportID: 0x01, Offset: 72, Size: 8, Value: 0 0.302305 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302315 Path: 00860004.Flow.iProduct, Type: Feature, ReportID: 0x01, Offset: 80, Size: 8, Value: 0 0.302320 Report[buf]: (13 bytes) => 08 03 4d 00 45 00 43 00 00 00 00 00 00 0.302325 Path: 00860004.Flow.iSerialNumber, Type: Feature, ReportID: 0x01, Offset: 88, Size: 8, Value: 0 0.307186 Report[get]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307201 Path: 00860004.Flow.FlowID, Type: Feature, ReportID: 0x02, Offset: 0, Size: 4, Value: 3e+07 0.307209 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307216 Path: 00860004.Flow.ConfigVoltage, Type: Feature, ReportID: 0x02, Offset: 8, Size: 16, Value: 77 0.307223 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307229 Path: 00860004.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 24, Size: 16, Value: 5 0.307241 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307248 Path: 00860004.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x02, Offset: 40, Size: 16, Value: 67 0.307261 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307266 Path: 00860004.Flow.ConfigActivePower, Type: Feature, ReportID: 0x02, Offset: 56, Size: 16, Value: 48 0.307276 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307282 Path: 00860004.Flow.DelayBeforeStartup, Type: Feature, ReportID: 0x02, Offset: 72, Size: 24, Value: 48 0.307288 Report[buf]: (16 bytes) => 10 03 4d 00 45 00 43 00 30 00 30 00 30 00 32 00 0.307307 Path: 00860004.Flow.DelayBeforeShutdown, Type: Feature, ReportID: 0x02, Offset: 96, Size: 24, Value: 12800 0.478190 Report[get]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478206 Path: 00860004.BatterySystem.BatterySystemID, Type: Feature, ReportID: 0x03, Offset: 0, Size: 4, Value: 3 0.478213 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478219 Path: 00860004.BatterySystem.PresentStatus.Used, Type: Feature, ReportID: 0x03, Offset: 8, Size: 1, Value: 1 0.478225 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478231 Path: 00860004.BatterySystem.PresentStatus.Good, Type: Feature, ReportID: 0x03, Offset: 9, Size: 1, Value: 0 0.478236 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478244 Path: 00860004.BatterySystem.Voltage, Type: Feature, ReportID: 0x03, Offset: 16, Size: 24, Value: 204.8 0.478256 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478263 Path: 00860004.BatterySystem.Temperature, Type: Feature, ReportID: 0x03, Offset: 40, Size: 16, Value: 8.3e+06 0.478269 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478276 Path: 00860004.BatterySystem.Test, Type: Input, ReportID: 0x03, Offset: 0, Size: 1, Value: 100000 0.478281 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.478291 Path: 00860004.BatterySystem.Test, Type: Feature, ReportID: 0x03, Offset: 56, Size: 1, Value: 0 0.490193 Report[get]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490209 Path: 00860004.PowerConverter.PowerConverterID, Type: Input, ReportID: 0x04, Offset: 0, Size: 4, Value: 300000 0.490216 Report[buf]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490223 Path: 00860004.PowerConverter.Input.InputID, Type: Input, ReportID: 0x04, Offset: 8, Size: 4, Value: 500000 0.490228 Report[buf]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490235 Path: 00860004.PowerConverter.Input.FlowID, Type: Input, ReportID: 0x04, Offset: 12, Size: 4, Value: 500000 0.490240 Report[buf]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490252 Path: 00860004.PowerConverter.Input.PresentStatus.Good, Type: Input, ReportID: 0x04, Offset: 16, Size: 1, Value: 0 0.490257 Report[buf]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490264 Path: 00860004.PowerConverter.Input.Voltage, Type: Input, ReportID: 0x04, Offset: 24, Size: 16, Value: 0.8 0.490270 Report[buf]: (8 bytes) => 16 03 55 00 50 00 53 00 0.490281 Path: 00860004.PowerConverter.Input.Frequency, Type: Input, ReportID: 0x04, Offset: 40, Size: 16, Value: 8.3e+06 0.508193 Report[get]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508253 Path: 00860004.PowerConverter.Output.OutputID, Type: Input, ReportID: 0x05, Offset: 0, Size: 4, Value: 300000 0.508264 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508358 Path: 00860004.PowerConverter.Output.FlowID, Type: Input, ReportID: 0x05, Offset: 4, Size: 4, Value: 0 0.508369 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508462 Path: 00860004.PowerConverter.Output.Voltage, Type: Input, ReportID: 0x05, Offset: 8, Size: 16, Value: 0.85 0.508472 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508568 Path: 00860004.PowerConverter.Output.Frequency, Type: Input, ReportID: 0x05, Offset: 24, Size: 16, Value: 8e+06 0.508575 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508582 Path: 00860004.PowerConverter.Output.PercentLoad, Type: Input, ReportID: 0x05, Offset: 40, Size: 16, Value: 8.3e+06 0.508592 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508681 Path: 00860004.PowerConverter.Output.PresentStatus.Overload, Type: Input, ReportID: 0x05, Offset: 56, Size: 1, Value: 0 0.508691 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508797 Path: 00860004.PowerConverter.Output.PresentStatus.Boost, Type: Input, ReportID: 0x05, Offset: 57, Size: 1, Value: 0 0.508807 Report[buf]: (9 bytes) => 16 03 55 00 50 00 53 00 20 0.508900 Path: 00860004.PowerConverter.Output.PresentStatus.Buck, Type: Input, ReportID: 0x05, Offset: 58, Size: 1, Value: 0 Network UPS Tools - Generic HID driver 0.41 (2.7.4) USB communication driver 0.33 0.508980 Report descriptor retrieved (Reportlen = 624) 0.508987 Found HID device 0.509036 Detected a UPS: MEC/MEC0002 0.509047 find_nut_info: unknown info type: load.off.delay 0.509103 find_nut_info: unknown info type: load.on.delay 0.509155 find_nut_info: unknown info type: load.off.delay 0.509212 upsdrv_initinfo... 0.509271 upsdrv_updateinfo... 0.761199 libusb_get_interrupt: Connection timed out 0.761220 Got 0 HID objects... 0.761227 Quick update... 0.761283 dstate_init: sock /var/run/nut/usbhid-ups-turbo-x open on fd 5 0.761299 upsdrv_updateinfo... 1.013199 libusb_get_interrupt: Connection timed out 1.013213 Got 0 HID objects... 1.013218 Quick update... 2.763063 upsdrv_updateinfo... 3.015236 libusb_get_interrupt: Connection timed out 3.015248 Got 0 HID objects... 3.015254 Quick update... 4.764823 upsdrv_updateinfo... 5.016274 libusb_get_interrupt: Connection timed out 5.016287 Got 0 HID objects... 5.016292 Quick update... 6.766584 upsdrv_updateinfo... 7.018312 libusb_get_interrupt: Connection timed out 7.018324 Got 0 HID objects... 7.018330 Quick update... 8.768346 upsdrv_updateinfo... 9.020354 libusb_get_interrupt: Connection timed out 9.020368 Got 0 HID objects... 9.020373 Quick update...> > The other PDC HID UPSes would usually report some changes every few > seconds. If you do not see any changes after "rebooting" the UPS > (something other than "Got 0 HID objects..."), try toggling the AC power > (recommend using a circuit breaker or power strip to keep the ground and > neutral attached) to see what an "on battery" event looks like. >Regards Vassilis Virvilis
Charles Lepple
2016-Sep-08 13:39 UTC
[Nut-upsuser] blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
On Sep 8, 2016, at 9:25 AM, Vassilis Virvilis <vasvir at iit.demokritos.gr> wrote:> > + failed to claim USB device: could not claim interface 0: Device or > resource busy > + detached kernel driver from USB device... > nut_usb_set_altinterface: skipped usb_set_altinterface(udev, 0) > HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 70 02 > > **** device or resource busy?This happens the first time you run a NUT driver after the USB cable is plugged in, or the system reboots. The old Linux kernel HID driver was not sufficient for reading UPS values (it could not tell the difference between an input voltage and an output voltage), so NUT detaches that driver and uses libusb instead. You could also try adding "-x usb_set_altinterface" to the command line (or adding it to ups.conf). The lsusb output implies that the only valid setting is 0 (bAlternateSetting), but it might need to be set explicitly.> 12) stripping, diffing -- no diffsIt might be useful to check and see if the vendor's suggested software actually works with this UPS, and if so, record some of the messages it sends.
Vassilis Virvilis
2016-Sep-08 14:05 UTC
[Nut-upsuser] blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
> You could also try adding "-x usb_set_altinterface" to the command line > (or adding it to ups.conf). The lsusb output implies that the only valid > setting is 0 (bAlternateSetting), but it might need to be set explicitly.I checked with -x usb_set_altinterface and it says nut_usb_set_altinterface: usb_set_altinterface() should not be necessary - please email the nut-upsdev list with information about your UPS no other difference from the previous runs> > It might be useful to check and see if the vendor's suggested software > actually works with this UPS, and if so, record some of the messages it > sends.Now that's a problem. I am not sure that I can find 1) the original software 2) a (physical) windows machine in the vicinity of the UPS I will give it a try but for now looks like a dead end. I have 3 of these UPS. Two of them have dead batteries and since they take 4 batteries each it makes it harder to justify their repair. If I find the software and a windows machine what software should I use to sniff the usb traffic? Thanks for your help so far. It was really insightful and educational. Regards Vassilis Virvilis
Maybe Matching Threads
- blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
- blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
- blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
- blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]
- blazer_usb MEC0002 problem Fry's Electronics (Turbo-X) [HID PDC?]