I set debug_min to 6 as suggested in your referenced doco.
The resulting log is attached.
Cheers and thanks,
Stephen
On 17/12/25 20:33, Jim Klimov wrote:> > Can't open /run/nut/nutdrv_qx-ups1: No such file or directory
>
> That's the driver checking if another instance of it is running. Newer
> releases should log it less frighteningly.
>
> > ... but nut-driver complained so...
>
> The `nut-driver at upsname` is a systemd instance wrapping an execution of
> a NUT driver program as a daemon. It is the driver program that actually
> complains, and its debug logs we want to see to figure out what puzzle
> pieces did not fit together.
>
> For an in-vivo debug bump (so the detailed logs end up in systemd
> journal) you can also temporarily set `debug_min` in the `ups.conf`, see
> https://github.com/networkupstools/nut/wiki/Changing-NUT-daemon-debug-
> verbosity <https://github.com/networkupstools/nut/wiki/Changing-NUT-
> daemon-debug-verbosity>?for more details (they varied from one NUT
> release to another).
>
> Jim
>
>
>
> On Wed, Dec 17, 2025 at 9:45?AM Stephen Davies <sdavies at sdc.com.au
> <mailto:sdavies at sdc.com.au>> wrote:
>
> Thanks for the feedback.
>
> The NUT vwersion is 2.8.2.1.
>
> I am in the process of building a new Rocky Linux 10 server after my
> old
> Centos 7 server died.
>
> The old box used upsSmart to access the UPS but that relies on an X
> server and does not work on ocky 10.
>
> One of the errors from your suggested test is:
>
> Can't open /run/nut/nutdrv_qx-ups1: No such file or directory
>
> I had "langid_fix=0x0409" in ups.conf but nut-driver
complained so I
> removed it.
>
> Cheers,
> Stephen
>
> On 17/12/25 18:47, Jim Klimov wrote:
> > Cheers,
> >
> >? ? What NUT version is involved? Per `nut-driver at ups1` I
suppose
> it is
> > some v2.8.x, and reports like https://github.com/networkupstools/
> nut/ <https://github.com/networkupstools/nut/>
> > pull/638 <https://github.com/networkupstools/nut/pull/638
> <https://github.com/networkupstools/nut/pull/638>> and
https://
> > github.com/networkupstools/nut/issues/674 <http://github.com/
> networkupstools/nut/issues/674> <https://github.com/ <https://
> github.com/>
> > networkupstools/nut/issues/674> suggest the needed support was
> merged
> > before v2.8.0, so that should suffice.
> >
> >? ? It may well be that the manufacturer moved on and stamped the
> same
> > label onto a completely unrelated device (or firmware), these
things
> > sadly tend to happen as products evolve.
> >
> >? ? One of those discussions starts with a "|Device not
supported|"
> > initially, but then it gets found "after opening and then
closing
> the
> > OEM software" (UPSmart), and apparently by the end of the
ticket
> they
> > got it working right away. The new hunnox subdriver introduced in
> PR 638
> > changed the initialization to work with that, per https://
> github.com/ <https://github.com/>
> > networkupstools/nut/pull/638#issuecomment-443558510 <https://
> github.com/ <https://github.com/>
> > networkupstools/nut/pull/638#issuecomment-443558510>?- notably
> there's a
> > sleep involved before the device returns valid info; maybe your
> device
> > or its firmware needs a longer one or something?
> >
> >? ? Compared to settings in those tickets and HCL, your setup
> misses a
> > `langid_fix=0x0409` line, not sure if that makes the difference.
> This
> > seems to be a hardcoded default in?hunnox_protocol() initializer
at
> > https://github.com/networkupstools/nut/pull/638/changes#diff-
> <https://github.com/networkupstools/nut/pull/638/changes#diff->
> >
> cb890ac7b82cb7a4f861284bcf39cc4f168312b61cb9455eb2755e345c0aa627R692-
> > R696 <https://github.com/networkupstools/nut/pull/638/
> changes#diff- <https://github.com/networkupstools/nut/pull/638/
> changes#diff->
> >
>
cb890ac7b82cb7a4f861284bcf39cc4f168312b61cb9455eb2755e345c0aa627R692-R696>
> >
> >? ? Can you start the driver with higher verbosity to collect
> what/how it
> > probes of the device, and how that fails (with what errors), e.g.
> >
> > |nutdrv_qx -a ups1 -d 1 -DDDDDD|
> >
> >? ? If there would be a long wall of text, maybe follow up with
> that as a
> > new GitHub issue?
> >
> > Hope this helps,
> > Jim Klimov
> >
> >
> >
> > On Wed, Dec 17, 2025 at 8:23?AM Stephen Davies via Nut-upsuser
<nut-
> > upsuser at alioth-lists.debian.net <mailto:upsuser at alioth-
> lists.debian.net> <mailto:nut-upsuser at alioth- <mailto:nut-
> upsuser at alioth->
> > lists.debian.net <http://lists.debian.net>>> wrote:
> >
> >? ? ?According to the support list, the Digitech 650VA UPS is
> supported but
> >? ? ?when I try to connect to my unit, I get:
> >? ? ?nut-driver at ups1[357464]: Device not supported!
> >
> >? ? ?My ips.conf has:
> >? ? ?[ups1]
> >? ? ?driver = nutdrv_qx
> >? ? ?port = auto
> >? ? ?vendorid=0001
> >? ? ?productid=0000
> >? ? ?protocol=hunnox
> >? ? ?novendor
> >? ? ?noscanlangid
> >
> >
> >
> >? ? ?_______________________________________________
> >? ? ?Nut-upsuser mailing list
> > Nut-upsuser at alioth-lists.debian.net <mailto:Nut-upsuser at
alioth-
> lists.debian.net> <mailto:Nut-upsuser at alioth- <mailto:Nut-
> upsuser at alioth->
> > lists.debian.net <http://lists.debian.net>>
> > https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-
> upsuser <https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/
> nut-upsuser>
> >? ? ?<https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/
> nut-upsuser <https://alioth-lists.debian.net/cgi-bin/mailman/
> listinfo/nut-upsuser>>
> >
>
-------------- next part --------------
Dec 19 18:04:00 mustang systemd[1]: Stopped nut-driver at ups1.service - Network
UPS Tools - device driver for ups1.
Dec 19 18:04:02 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:07 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:12 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:17 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:22 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:27 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:32 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:37 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:40 mustang systemd[1]: Starting nut-driver at ups1.service -
Network UPS Tools - device driver for ups1...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: Network UPS Tools - UPS
driver controller 2.8.2.1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: Network UPS Tools - Generic
Q* USB/Serial driver 0.36 (2.8.2.1)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: USB communication driver
(libusb 1.0) 0.48
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.000000#011[D1] debug
level is '6'
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.000013#011[D5]
send_to_all: SETINFO driver.debug "6"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.000019#011[D5]
send_to_all: SETFLAGS driver.debug RW NUMBER
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001028#011[D1] Succeeded
to become_user(nut): now UID=57 GID=57
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001051#011[D1]
Signalling UPS [ups1]: driver.exit (quietly, no fuss if no driver is running or
responding)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001065#011Can't open
/run/nut/nutdrv_qx-ups1: No such file or directory
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001076#011[D1] Request
for other driver to exit returned code -1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001082#011[D1] Socket
dialog with the other driver instance (may be absent) failed: No such file or
directory
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001091#011[D1] PID file
/run/nut/nutdrv_qx-ups1.pid not found; stat() returned -1 (errno=2): No such
file or directory
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001124#011[D1] Saving
PID 916125 into /run/nut/nutdrv_qx-ups1.pid
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001152#011[D5]
send_to_all: SETINFO device.type "ups"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001158#011[D5]
send_to_all: SETINFO driver.state "init.device"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.001162#011[D1]
upsdrv_initups...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005240#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005264#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005267#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005273#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005276#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005282#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.005285#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.006554#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.007734#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008949#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008961#011[D2] -
VendorID: 0001
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008963#011[D2] -
ProductID: 0000
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008966#011[D2] -
Manufacturer: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008968#011[D2] -
Product: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008971#011[D2] - Serial
Number: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008974#011[D2] - Bus:
003
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008977#011[D2] - Bus
Port: 006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008980#011[D2] - Device:
006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008984#011[D2] - Device
release number: 0100
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008987#011[D2] Trying to
match device
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.008990#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009022#011[D2] Device
matches
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009025#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009033#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009053#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009058#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009065#011[D5]
send_to_all: SETINFO ups.vendorid "0001"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009069#011[D5]
send_to_all: SETINFO ups.productid "0000"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009073#011[D2] Skipping
protocol Voltronic 0.08
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009076#011[D2] Skipping
protocol Voltronic-QS 0.09
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009078#011[D2] Skipping
protocol Voltronic-QS-Hex 0.10
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009080#011[D2] Skipping
protocol Mustek 0.08
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009082#011[D2] Skipping
protocol Megatec/old 0.08
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009085#011[D2] Skipping
protocol BestUPS 0.07
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009087#011[D2] Skipping
protocol Mecer 0.08
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009089#011[D2] Skipping
protocol Megatec 0.07
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009091#011[D2] Skipping
protocol Zinto 0.07
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009093#011[D2] Skipping
protocol Masterguard 0.02
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.009104#011[D3] send: Q1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.010386#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.010400#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.010528#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014823#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014838#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014843#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014849#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014854#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014860#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.014863#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.016056#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.017244#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018443#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018459#011[D2] -
VendorID: 0001
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018462#011[D2] -
ProductID: 0000
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018465#011[D2] -
Manufacturer: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018468#011[D2] -
Product: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018471#011[D2] - Serial
Number: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018474#011[D2] - Bus:
003
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018476#011[D2] - Bus
Port: 006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018479#011[D2] - Device:
006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018482#011[D2] - Device
release number: 0100
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018485#011[D2] Trying to
match device
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018488#011[D3]
match_function_exact: matching a device...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018490#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018499#011[D2] Device
matches
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018502#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018510#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018527#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018531#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018539#011[D5]
send_to_all: SETINFO driver.state "reconnect.updateinfo"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.018543#011[D3] send: Q1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.019696#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.019703#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.019770#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024692#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024708#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024713#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024721#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024724#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024729#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.024733#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.025964#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.027138#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028359#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028372#011[D2] -
VendorID: 0001
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028379#011[D2] -
ProductID: 0000
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028381#011[D2] -
Manufacturer: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028384#011[D2] -
Product: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028387#011[D2] - Serial
Number: unknown
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028390#011[D2] - Bus:
003
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028393#011[D2] - Bus
Port: 006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028396#011[D2] - Device:
006
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028400#011[D2] - Device
release number: 0100
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028403#011[D2] Trying to
match device
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028406#011[D3]
match_function_exact: matching a device...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028410#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028416#011[D2] Device
matches
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028419#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028424#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028435#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028439#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028445#011[D5]
send_to_all: SETINFO driver.state "reconnect.updateinfo"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.028448#011[D3] send: Q1
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029620#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029625#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029690#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029696#011[D2] Skipping
protocol Ablerex 0.01
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029700#011[D2] Skipping
protocol Q1 0.08
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029703#011Device not
supported!
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029706#011Device not
supported!
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029711#011[D5]
send_to_all: SETINFO driver.state "cleanup.exit"
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029716#011[D6]
upsnotify: notify about state 4 with libsystemd: use sd_notify()
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: 0.029720#011[D6]
upsnotify: posting sd_notify: STATUS=exit_cleanup()
Dec 19 18:04:41 mustang nut-driver at ups1[916125]: STOPPING=1
Dec 19 18:04:41 mustang systemd[1]: nut-driver at ups1.service: Main process
exited, code=exited, status=1/FAILURE
Dec 19 18:04:41 mustang systemd[1]: nut-driver at ups1.service: Failed with
result 'exit-code'.
Dec 19 18:04:41 mustang systemd[1]: Failed to start nut-driver at ups1.service -
Network UPS Tools - device driver for ups1.
Dec 19 18:04:41 mustang nut-server[342574]: Can't connect to UPS [ups1]
(nutdrv_qx-ups1): No such file or directory
Dec 19 18:04:41 mustang upsd[342574]: Can't connect to UPS [ups1]
(nutdrv_qx-ups1): No such file or directory
Dec 19 18:04:42 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:47 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:52 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected
Dec 19 18:04:56 mustang systemd[1]: nut-driver at ups1.service: Scheduled
restart job, restart counter is at 1.
Dec 19 18:04:56 mustang systemd[1]: Starting nut-driver at ups1.service -
Network UPS Tools - device driver for ups1...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: Network UPS Tools - UPS
driver controller 2.8.2.1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: Network UPS Tools - Generic
Q* USB/Serial driver 0.36 (2.8.2.1)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: USB communication driver
(libusb 1.0) 0.48
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000000#011[D1] debug
level is '6'
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000016#011[D5]
send_to_all: SETINFO driver.debug "6"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000023#011[D5]
send_to_all: SETFLAGS driver.debug RW NUMBER
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000821#011[D1] Succeeded
to become_user(nut): now UID=57 GID=57
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000836#011[D1]
Signalling UPS [ups1]: driver.exit (quietly, no fuss if no driver is running or
responding)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000846#011Can't open
/run/nut/nutdrv_qx-ups1: No such file or directory
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000851#011[D1] Request
for other driver to exit returned code -1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000854#011[D1] Socket
dialog with the other driver instance (may be absent) failed: No such file or
directory
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000860#011[D1] PID file
/run/nut/nutdrv_qx-ups1.pid not found; stat() returned -1 (errno=2): No such
file or directory
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000883#011[D1] Saving
PID 916173 into /run/nut/nutdrv_qx-ups1.pid
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000902#011[D5]
send_to_all: SETINFO device.type "ups"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000905#011[D5]
send_to_all: SETINFO driver.state "init.device"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.000907#011[D1]
upsdrv_initups...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004841#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004858#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004863#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004869#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004872#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004877#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.004879#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.006092#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.007280#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008480#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008493#011[D2] -
VendorID: 0001
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008498#011[D2] -
ProductID: 0000
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008500#011[D2] -
Manufacturer: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008503#011[D2] -
Product: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008506#011[D2] - Serial
Number: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008510#011[D2] - Bus:
003
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008513#011[D2] - Bus
Port: 006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008516#011[D2] - Device:
006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008520#011[D2] - Device
release number: 0100
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008523#011[D2] Trying to
match device
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008527#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008557#011[D2] Device
matches
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008561#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008568#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008590#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008594#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008601#011[D5]
send_to_all: SETINFO ups.vendorid "0001"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008605#011[D5]
send_to_all: SETINFO ups.productid "0000"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008609#011[D2] Skipping
protocol Voltronic 0.08
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008611#011[D2] Skipping
protocol Voltronic-QS 0.09
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008614#011[D2] Skipping
protocol Voltronic-QS-Hex 0.10
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008616#011[D2] Skipping
protocol Mustek 0.08
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008619#011[D2] Skipping
protocol Megatec/old 0.08
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008621#011[D2] Skipping
protocol BestUPS 0.07
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008624#011[D2] Skipping
protocol Mecer 0.08
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008626#011[D2] Skipping
protocol Megatec 0.07
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008628#011[D2] Skipping
protocol Zinto 0.07
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008631#011[D2] Skipping
protocol Masterguard 0.02
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.008635#011[D3] send: Q1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.009876#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.009883#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.009978#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014604#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014619#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014625#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014631#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014635#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014640#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.014644#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.015872#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.017030#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018204#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018217#011[D2] -
VendorID: 0001
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018223#011[D2] -
ProductID: 0000
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018226#011[D2] -
Manufacturer: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018229#011[D2] -
Product: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018233#011[D2] - Serial
Number: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018236#011[D2] - Bus:
003
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018239#011[D2] - Bus
Port: 006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018242#011[D2] - Device:
006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018246#011[D2] - Device
release number: 0100
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018249#011[D2] Trying to
match device
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018252#011[D3]
match_function_exact: matching a device...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018255#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018263#011[D2] Device
matches
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018266#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018272#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018287#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018291#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018298#011[D5]
send_to_all: SETINFO driver.state "reconnect.updateinfo"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.018301#011[D3] send: Q1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.019481#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.019496#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.019598#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024494#011[D2] Checking
device 1 of 8 (1D6B/0003)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024507#011[D1] Failed to
open device (1D6B/0003), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024511#011[D2] Checking
device 2 of 8 (17EF/6190)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024518#011[D1] Failed to
open device (17EF/6190), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024520#011[D2] Checking
device 3 of 8 (17EF/608D)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024525#011[D1] Failed to
open device (17EF/608D), skipping: Access denied (insufficient permissions)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.024527#011[D2] Checking
device 4 of 8 (0001/0000)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.025734#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.026905#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028052#011[D1]
nut_libusb_open get iProduct failed, retrying...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028057#011[D2] -
VendorID: 0001
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028061#011[D2] -
ProductID: 0000
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028064#011[D2] -
Manufacturer: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028067#011[D2] -
Product: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028069#011[D2] - Serial
Number: unknown
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028071#011[D2] - Bus:
003
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028074#011[D2] - Bus
Port: 006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028076#011[D2] - Device:
006
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028078#011[D2] - Device
release number: 0100
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028081#011[D2] Trying to
match device
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028083#011[D3]
match_function_exact: matching a device...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028085#011[D3]
match_function_regex: matching a device...
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028091#011[D2] Device
matches
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028093#011[D2] Reading
configuration descriptor 1 of 1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028098#011[D3]
libusb_kernel_driver_active() returned 0: Success
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028111#011[D2] Claimed
interface 0 successfully
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028115#011[D3]
nut_usb_set_altinterface: skipped libusb_set_interface_alt_setting(udev, 0, 0)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028122#011[D5]
send_to_all: SETINFO driver.state "reconnect.updateinfo"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.028125#011[D3] send: Q1
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029292#011[D3] read:
Input/Output Error (-1)
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029308#011[D5]
send_to_all: SETINFO driver.state "reconnect.trying"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029395#011[D4]
qx_process: failed to preprocess answer [input.voltage]
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029401#011[D2] Skipping
protocol Ablerex 0.01
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029404#011[D2] Skipping
protocol Q1 0.08
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029407#011Device not
supported!
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029411#011Device not
supported!
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029415#011[D5]
send_to_all: SETINFO driver.state "cleanup.exit"
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029420#011[D6]
upsnotify: notify about state 4 with libsystemd: use sd_notify()
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: 0.029423#011[D6]
upsnotify: posting sd_notify: STATUS=exit_cleanup()
Dec 19 18:04:56 mustang nut-driver at ups1[916173]: STOPPING=1
Dec 19 18:04:56 mustang systemd[1]: nut-driver at ups1.service: Main process
exited, code=exited, status=1/FAILURE
Dec 19 18:04:56 mustang systemd[1]: nut-driver at ups1.service: Failed with
result 'exit-code'.
Dec 19 18:04:56 mustang systemd[1]: Failed to start nut-driver at ups1.service -
Network UPS Tools - device driver for ups1.
Dec 19 18:04:57 mustang nut-monitor[105815]: Poll UPS [ups1 at localhost] failed
- Driver not connected