Brady Chang
2006-Mar-01  08:12 UTC
[Nut-upsuser] tripplite SMART3000RM2U ups.status never change
Hello, I was wonder if anybody experienced this problem or any recommendation on troubleshooting the problem. unplug power, ups.status does not change. fedora core 4 kernel 2.6.13-1.1532_FC4smp, binary compiled from latest 2.0.3 src thanks in advance. battery.charge: 100.0 battery.voltage: 005.1 driver.name: snmp-ups driver.parameter.mibs: ietf driver.parameter.pollfreq: 15 driver.parameter.port: ups01 driver.parameter.snmp_version: v2c driver.version: 2.0.3 driver.version.internal: 0.41 input.voltage: 000.0 ups.firmware.aux: 12.03.0024 ups.load: 068.0 ups.mfr: Tripp Lite ups.model: SMART3000RM2U ups.status: OL battery.charge: 050.0 battery.voltage: 004.4 driver.name: snmp-ups driver.parameter.mibs: ietf driver.parameter.pollfreq: 15 driver.parameter.port: ups01 driver.parameter.snmp_version: v2c driver.version: 2.0.3 driver.version.internal: 0.41 input.voltage: 000.0 ups.firmware.aux: 12.03.0024 ups.load: 067.0 ups.mfr: Tripp Lite ups.model: SMART3000RM2U ups.status: OL -------------- next part -------------- An HTML attachment was scrubbed... URL: http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20060228/1f43c781/attachment.html
Niels Baggesen
2006-Mar-01  08:20 UTC
[Nut-upsuser] tripplite SMART3000RM2U ups.status never change
On Tue, Feb 28, 2006 at 08:46:41PM -0600, Brady Chang wrote:> > Hello, I was wonder if anybody experienced this problem or any recommendation on troubleshooting the problem. > unplug power, ups.status does not change. fedora core 4 kernel 2.6.13-1.1532_FC4smp, binary compiled from latest 2.0.3 srcWhat does an snmpwalk of the ups show? /Niels -- Niels Baggesen - @home - ?rhus - Denmark - nba@users.sourceforge.net The purpose of computing is insight, not numbers --- R W Hamming
Niels Baggesen
2006-Mar-01  19:21 UTC
[Nut-upsuser] tripplite SMART3000RM2U ups.status never change
On Wed, Mar 01, 2006 at 08:26:02AM -0600, Brady Chang wrote:> SNMPv2-SMI::mib-2.33.1.4.1.0 = INTEGER: 3This one is the crucial one ... If we translate it using the MIB it is $ snmptranslate -Td -m+UPS-MIB SNMPv2-SMI::mib-2.33.1.4.1.0 UPS-MIB::upsOutputSource.0 upsOutputSource OBJECT-TYPE -- FROM UPS-MIB SYNTAX INTEGER {other(1), none(2), normal(3), bypass(4), battery(5), booster(6), reducer(7)} MAX-ACCESS read-only STATUS current DESCRIPTION "The present source of output power. The enumeration none(2) indicates that there is no source of output power (and therefore no output power), for example, the system has opened the output breaker." ::= { iso(1) org(3) dod(6) internet(1) mgmt(2) mib-2(1) upsMIB(33) upsObjects(1) upsOutput(4) upsOutputSource(1) 0 } or UPS-MIB::upsOutputSource.0 = INTEGER: normal(3) So the UPS does not say that it is on battery, which means that there is no way for NUT to say it /Niels -- Niels Baggesen - @home - ?rhus - Denmark - nba@users.sourceforge.net The purpose of computing is insight, not numbers --- R W Hamming
Brady Chang
2006-Mar-02  16:07 UTC
[Nut-upsuser] tripplite SMART3000RM2U ups.status never change
Thanks for the reply snmpwalk -v 2c -c private ups01 >walk.out # cat walk.out SNMPv2-MIB::sysDescr.0 = STRING: POWERALERT 12 SNMPv2-MIB::sysObjectID.0 = OID: SNMPv2-SMI::enterprises.850.1 SNMPv2-MIB::sysUpTime.0 = Timeticks: (87465657) 10 days, 2:57:36.57 SNMPv2-MIB::sysContact.0 = STRING: www.tripplite.com SNMPv2-MIB::sysName.0 = STRING: Tripp Lite SNMPv2-MIB::sysLocation.0 = STRING: 1111 W. 35th St., Chicago IL, 60609 SNMPv2-MIB::sysServices.0 = INTEGER: 72 SNMPv2-MIB::sysORLastChange.0 = Timeticks: (10772873) 1 day, 5:55:28.73 SNMPv2-MIB::sysORID.1 = OID: SNMPv2-MIB::sysOREntry SNMPv2-MIB::sysORDescr.1 = STRING: The sysORTable capabilities are still being explored. It appears that the AGENT-CAPABILITIES macro in the MIB definitions should be used to generate these table entries. See RFC2580 SNMPv2-MIB::sysORUpTime.1 = Timeticks: (10772873) 1 day, 5:55:28.73 IF-MIB::ifNumber.0 = INTEGER: 4 IF-MIB::ifIndex.1 = INTEGER: 1 IF-MIB::ifIndex.2 = INTEGER: 2 IF-MIB::ifIndex.3 = INTEGER: 3 IF-MIB::ifIndex.4 = INTEGER: 4 IF-MIB::ifDescr.1 = STRING: lo IF-MIB::ifDescr.2 = STRING: eth0 IF-MIB::ifDescr.3 = STRING: ppp0 IF-MIB::ifDescr.4 = STRING: ppp1 IF-MIB::ifType.1 = INTEGER: other(1) IF-MIB::ifType.2 = INTEGER: iso88023Csmacd(7) IF-MIB::ifType.3 = INTEGER: ppp(23) IF-MIB::ifType.4 = INTEGER: ppp(23) IF-MIB::ifMtu.1 = INTEGER: 1500 IF-MIB::ifMtu.2 = INTEGER: 1500 IF-MIB::ifMtu.3 = INTEGER: 1500 IF-MIB::ifMtu.4 = INTEGER: 1500 IF-MIB::ifSpeed.1 = Gauge32: 0 IF-MIB::ifSpeed.2 = Gauge32: 100000000 IF-MIB::ifSpeed.3 = Gauge32: 9600 IF-MIB::ifSpeed.4 = Gauge32: 9600 IF-MIB::ifPhysAddress.1 = STRING: 0 IF-MIB::ifPhysAddress.2 = STRING: 0:6:67:20:65:52 IF-MIB::ifPhysAddress.3 = STRING: 0 IF-MIB::ifPhysAddress.4 = STRING: 0 IF-MIB::ifAdminStatus.1 = INTEGER: up(1) IF-MIB::ifAdminStatus.2 = INTEGER: up(1) IF-MIB::ifAdminStatus.3 = INTEGER: down(2) IF-MIB::ifAdminStatus.4 = INTEGER: down(2) IF-MIB::ifOperStatus.1 = INTEGER: up(1) IF-MIB::ifOperStatus.2 = INTEGER: up(1) IF-MIB::ifOperStatus.3 = INTEGER: down(2) IF-MIB::ifOperStatus.4 = INTEGER: down(2) IF-MIB::ifLastChange.1 = Timeticks: (0) 0:00:00.00 IF-MIB::ifLastChange.2 = Timeticks: (0) 0:00:00.00 IF-MIB::ifLastChange.3 = Timeticks: (0) 0:00:00.00 IF-MIB::ifLastChange.4 = Timeticks: (0) 0:00:00.00 IF-MIB::ifInOctets.1 = Counter32: 0 IF-MIB::ifInOctets.2 = Counter32: 256355421 IF-MIB::ifInOctets.3 = Counter32: 0 IF-MIB::ifInOctets.4 = Counter32: 0 IF-MIB::ifInUcastPkts.1 = Counter32: 0 IF-MIB::ifInUcastPkts.2 = Counter32: 73216 IF-MIB::ifInUcastPkts.3 = Counter32: 0 IF-MIB::ifInUcastPkts.4 = Counter32: 0 IF-MIB::ifInNUcastPkts.1 = Counter32: 0 IF-MIB::ifInNUcastPkts.2 = Counter32: 3554340 IF-MIB::ifInNUcastPkts.3 = Counter32: 0 IF-MIB::ifInNUcastPkts.4 = Counter32: 0 IF-MIB::ifInDiscards.1 = Counter32: 0 IF-MIB::ifInDiscards.2 = Counter32: 0 IF-MIB::ifInDiscards.3 = Counter32: 0 IF-MIB::ifInDiscards.4 = Counter32: 0 IF-MIB::ifInErrors.1 = Counter32: 0 IF-MIB::ifInErrors.2 = Counter32: 3312557 IF-MIB::ifInErrors.3 = Counter32: 0 IF-MIB::ifInErrors.4 = Counter32: 0 IF-MIB::ifInUnknownProtos.1 = Counter32: 0 IF-MIB::ifInUnknownProtos.2 = Counter32: 0 IF-MIB::ifInUnknownProtos.3 = Counter32: 0 IF-MIB::ifInUnknownProtos.4 = Counter32: 0 IF-MIB::ifOutOctets.1 = Counter32: 0 IF-MIB::ifOutOctets.2 = Counter32: 9627844 IF-MIB::ifOutOctets.3 = Counter32: 0 IF-MIB::ifOutOctets.4 = Counter32: 0 IF-MIB::ifOutUcastPkts.1 = Counter32: 0 IF-MIB::ifOutUcastPkts.2 = Counter32: 72171 IF-MIB::ifOutUcastPkts.3 = Counter32: 0 IF-MIB::ifOutUcastPkts.4 = Counter32: 0 IF-MIB::ifOutNUcastPkts.1 = Counter32: 0 IF-MIB::ifOutNUcastPkts.2 = Counter32: 6281 IF-MIB::ifOutNUcastPkts.3 = Counter32: 0 IF-MIB::ifOutNUcastPkts.4 = Counter32: 0 IF-MIB::ifOutDiscards.1 = Counter32: 0 IF-MIB::ifOutDiscards.2 = Counter32: 0 IF-MIB::ifOutDiscards.3 = Counter32: 0 IF-MIB::ifOutDiscards.4 = Counter32: 0 IF-MIB::ifOutErrors.1 = Counter32: 0 IF-MIB::ifOutErrors.2 = Counter32: 0 IF-MIB::ifOutErrors.3 = Counter32: 0 IF-MIB::ifOutErrors.4 = Counter32: 0 IF-MIB::ifOutQLen.1 = Gauge32: 0 IF-MIB::ifOutQLen.2 = Gauge32: 0 IF-MIB::ifOutQLen.3 = Gauge32: 0 IF-MIB::ifOutQLen.4 = Gauge32: 0 IF-MIB::ifSpecific.1 = OID: SNMPv2-SMI::zeroDotZero IF-MIB::ifSpecific.2 = OID: SNMPv2-SMI::zeroDotZero IF-MIB::ifSpecific.3 = OID: SNMPv2-SMI::zeroDotZero IF-MIB::ifSpecific.4 = OID: SNMPv2-SMI::zeroDotZero RFC1213-MIB::atIfIndex.2.1.172.16.0.2 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.3 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.4 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.5 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.6 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.7 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.8 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.9 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.10 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.11 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.12 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.13 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.14 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.15 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.16 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.17 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.18 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.19 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.20 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.21 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.22 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.23 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.24 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.25 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.26 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.27 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.28 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.29 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.30 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.0.31 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.10.1 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.10.2 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.10.20 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.100.1 = INTEGER: 2 RFC1213-MIB::atIfIndex.2.1.172.16.149.244 = INTEGER: 2 RFC1213-MIB::atPhysAddress.2.1.172.16.0.2 = Hex-STRING: 00 13 D3 05 16 1F RFC1213-MIB::atPhysAddress.2.1.172.16.0.3 = Hex-STRING: 00 13 D3 05 17 E3 RFC1213-MIB::atPhysAddress.2.1.172.16.0.4 = Hex-STRING: 00 13 D3 05 17 CA RFC1213-MIB::atPhysAddress.2.1.172.16.0.5 = Hex-STRING: 00 13 D3 05 16 49 RFC1213-MIB::atPhysAddress.2.1.172.16.0.6 = Hex-STRING: 00 13 D3 05 15 E7 RFC1213-MIB::atPhysAddress.2.1.172.16.0.7 = Hex-STRING: 00 13 D3 05 16 4D RFC1213-MIB::atPhysAddress.2.1.172.16.0.8 = Hex-STRING: 00 13 D3 05 16 7B RFC1213-MIB::atPhysAddress.2.1.172.16.0.9 = Hex-STRING: 00 13 D3 05 16 71 RFC1213-MIB::atPhysAddress.2.1.172.16.0.10 = Hex-STRING: 00 13 D3 05 17 84 RFC1213-MIB::atPhysAddress.2.1.172.16.0.11 = Hex-STRING: 00 13 D3 05 17 68 RFC1213-MIB::atPhysAddress.2.1.172.16.0.12 = Hex-STRING: 00 13 D3 05 17 17 RFC1213-MIB::atPhysAddress.2.1.172.16.0.13 = Hex-STRING: 00 13 D3 05 17 7A RFC1213-MIB::atPhysAddress.2.1.172.16.0.14 = Hex-STRING: 00 13 D3 05 16 33 RFC1213-MIB::atPhysAddress.2.1.172.16.0.15 = Hex-STRING: 00 13 D3 05 16 31 RFC1213-MIB::atPhysAddress.2.1.172.16.0.16 = Hex-STRING: 00 13 D3 05 16 27 RFC1213-MIB::atPhysAddress.2.1.172.16.0.17 = Hex-STRING: 00 13 D3 05 17 B4 RFC1213-MIB::atPhysAddress.2.1.172.16.0.18 = Hex-STRING: 00 13 D3 05 17 6C RFC1213-MIB::atPhysAddress.2.1.172.16.0.19 = Hex-STRING: 00 13 D3 05 16 39 RFC1213-MIB::atPhysAddress.2.1.172.16.0.20 = Hex-STRING: 00 13 D3 05 16 59 RFC1213-MIB::atPhysAddress.2.1.172.16.0.21 = Hex-STRING: 00 13 D3 05 17 92 RFC1213-MIB::atPhysAddress.2.1.172.16.0.22 = Hex-STRING: 00 13 D3 05 16 1B RFC1213-MIB::atPhysAddress.2.1.172.16.0.23 = Hex-STRING: 00 13 D3 05 15 E9 RFC1213-MIB::atPhysAddress.2.1.172.16.0.24 = Hex-STRING: 00 13 D3 05 16 7D RFC1213-MIB::atPhysAddress.2.1.172.16.0.25 = Hex-STRING: 00 13 D3 05 17 BE RFC1213-MIB::atPhysAddress.2.1.172.16.0.26 = Hex-STRING: 00 13 D3 05 17 9C RFC1213-MIB::atPhysAddress.2.1.172.16.0.27 = Hex-STRING: 00 13 D3 05 16 83 RFC1213-MIB::atPhysAddress.2.1.172.16.0.28 = Hex-STRING: 00 13 D3 05 16 19 RFC1213-MIB::atPhysAddress.2.1.172.16.0.29 = Hex-STRING: 00 13 D3 05 17 8E RFC1213-MIB::atPhysAddress.2.1.172.16.0.30 = Hex-STRING: 00 13 D3 05 17 60 RFC1213-MIB::atPhysAddress.2.1.172.16.0.31 = Hex-STRING: 00 13 D3 05 16 35 RFC1213-MIB::atPhysAddress.2.1.172.16.10.1 = Hex-STRING: 00 E0 81 65 36 CB RFC1213-MIB::atPhysAddress.2.1.172.16.10.2 = Hex-STRING: 00 E0 81 65 35 1B RFC1213-MIB::atPhysAddress.2.1.172.16.10.20 = Hex-STRING: 00 E0 81 26 6E 80 RFC1213-MIB::atPhysAddress.2.1.172.16.100.1 = Hex-STRING: 00 13 D3 8C F9 D6 RFC1213-MIB::atPhysAddress.2.1.172.16.149.244 = Hex-STRING: 00 06 12 02 42 A0 RFC1213-MIB::atNetAddress.2.1.172.16.0.2 = Network Address: AC:10:00:02 RFC1213-MIB::atNetAddress.2.1.172.16.0.3 = Network Address: AC:10:00:03 RFC1213-MIB::atNetAddress.2.1.172.16.0.4 = Network Address: AC:10:00:04 RFC1213-MIB::atNetAddress.2.1.172.16.0.5 = Network Address: AC:10:00:05 RFC1213-MIB::atNetAddress.2.1.172.16.0.6 = Network Address: AC:10:00:06 RFC1213-MIB::atNetAddress.2.1.172.16.0.7 = Network Address: AC:10:00:07 RFC1213-MIB::atNetAddress.2.1.172.16.0.8 = Network Address: AC:10:00:08 RFC1213-MIB::atNetAddress.2.1.172.16.0.9 = Network Address: AC:10:00:09 RFC1213-MIB::atNetAddress.2.1.172.16.0.10 = Network Address: AC:10:00:0A RFC1213-MIB::atNetAddress.2.1.172.16.0.11 = Network Address: AC:10:00:0B RFC1213-MIB::atNetAddress.2.1.172.16.0.12 = Network Address: AC:10:00:0C RFC1213-MIB::atNetAddress.2.1.172.16.0.13 = Network Address: AC:10:00:0D RFC1213-MIB::atNetAddress.2.1.172.16.0.14 = Network Address: AC:10:00:0E RFC1213-MIB::atNetAddress.2.1.172.16.0.15 = Network Address: AC:10:00:0F RFC1213-MIB::atNetAddress.2.1.172.16.0.16 = Network Address: AC:10:00:10 RFC1213-MIB::atNetAddress.2.1.172.16.0.17 = Network Address: AC:10:00:11 RFC1213-MIB::atNetAddress.2.1.172.16.0.18 = Network Address: AC:10:00:12 RFC1213-MIB::atNetAddress.2.1.172.16.0.19 = Network Address: AC:10:00:13 RFC1213-MIB::atNetAddress.2.1.172.16.0.20 = Network Address: AC:10:00:14 RFC1213-MIB::atNetAddress.2.1.172.16.0.21 = Network Address: AC:10:00:15 RFC1213-MIB::atNetAddress.2.1.172.16.0.22 = Network Address: AC:10:00:16 RFC1213-MIB::atNetAddress.2.1.172.16.0.23 = Network Address: AC:10:00:17 RFC1213-MIB::atNetAddress.2.1.172.16.0.24 = Network Address: AC:10:00:18 RFC1213-MIB::atNetAddress.2.1.172.16.0.25 = Network Address: AC:10:00:19 RFC1213-MIB::atNetAddress.2.1.172.16.0.26 = Network Address: AC:10:00:1A RFC1213-MIB::atNetAddress.2.1.172.16.0.27 = Network Address: AC:10:00:1B RFC1213-MIB::atNetAddress.2.1.172.16.0.28 = Network Address: AC:10:00:1C RFC1213-MIB::atNetAddress.2.1.172.16.0.29 = Network Address: AC:10:00:1D RFC1213-MIB::atNetAddress.2.1.172.16.0.30 = Network Address: AC:10:00:1E RFC1213-MIB::atNetAddress.2.1.172.16.0.31 = Network Address: AC:10:00:1F RFC1213-MIB::atNetAddress.2.1.172.16.10.1 = Network Address: AC:10:0A:01 RFC1213-MIB::atNetAddress.2.1.172.16.10.2 = Network Address: AC:10:0A:02 RFC1213-MIB::atNetAddress.2.1.172.16.10.20 = Network Address: AC:10:0A:14 RFC1213-MIB::atNetAddress.2.1.172.16.100.1 = Network Address: AC:10:64:01 RFC1213-MIB::atNetAddress.2.1.172.16.149.244 = Network Address: AC:10:95:F4 IP-MIB::ipForwarding.0 = INTEGER: forwarding(1) IP-MIB::ipDefaultTTL.0 = INTEGER: 60 IP-MIB::ipInReceives.0 = Counter32: 68592 IP-MIB::ipInHdrErrors.0 = Counter32: 0 IP-MIB::ipInAddrErrors.0 = Counter32: 0 IP-MIB::ipForwDatagrams.0 = Counter32: 0 IP-MIB::ipInUnknownProtos.0 = Counter32: 0 IP-MIB::ipInDiscards.0 = Counter32: 0 IP-MIB::ipInDelivers.0 = Counter32: 68598 IP-MIB::ipOutRequests.0 = Counter32: 68892 IP-MIB::ipOutDiscards.0 = Counter32: 0 IP-MIB::ipOutNoRoutes.0 = Counter32: 0 IP-MIB::ipReasmTimeout.0 = INTEGER: 60 IP-MIB::ipReasmReqds.0 = Counter32: 0 IP-MIB::ipReasmOKs.0 = Counter32: 0 IP-MIB::ipReasmFails.0 = Counter32: 0 IP-MIB::ipFragOKs.0 = Counter32: 0 IP-MIB::ipFragFails.0 = Counter32: 0 IP-MIB::ipFragCreates.0 = Counter32: 0 IP-MIB::ipAdEntAddr.127.0.0.1 = IpAddress: 127.0.0.1 IP-MIB::ipAdEntAddr.172.16.149.242 = IpAddress: 172.16.149.242 IP-MIB::ipAdEntIfIndex.127.0.0.1 = INTEGER: 1 IP-MIB::ipAdEntIfIndex.172.16.149.242 = INTEGER: 2 IP-MIB::ipAdEntNetMask.127.0.0.1 = IpAddress: 255.0.0.0 IP-MIB::ipAdEntNetMask.172.16.149.242 = IpAddress: 255.255.0.0 IP-MIB::ipAdEntBcastAddr.127.0.0.1 = INTEGER: 1 IP-MIB::ipAdEntBcastAddr.172.16.149.242 = INTEGER: 1 IP-MIB::ipAdEntReasmMaxSize.127.0.0.1 = INTEGER: 65535 IP-MIB::ipAdEntReasmMaxSize.172.16.149.242 = INTEGER: 65535 RFC1213-MIB::ipRouteDest.0.0.0.0 = IpAddress: 0.0.0.0 RFC1213-MIB::ipRouteDest.127.0.0.0 = IpAddress: 127.0.0.0 RFC1213-MIB::ipRouteDest.172.16.0.0 = IpAddress: 172.16.0.0 RFC1213-MIB::ipRouteIfIndex.0.0.0.0 = INTEGER: 2 RFC1213-MIB::ipRouteIfIndex.127.0.0.0 = INTEGER: 1 RFC1213-MIB::ipRouteIfIndex.172.16.0.0 = INTEGER: 2 RFC1213-MIB::ipRouteMetric1.0.0.0.0 = INTEGER: 1 RFC1213-MIB::ipRouteMetric1.127.0.0.0 = INTEGER: 1 RFC1213-MIB::ipRouteMetric1.172.16.0.0 = INTEGER: 1 RFC1213-MIB::ipRouteMetric2.0.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric2.127.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric2.172.16.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric3.0.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric3.127.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric3.172.16.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric4.0.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric4.127.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric4.172.16.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteNextHop.0.0.0.0 = IpAddress: 172.16.100.1 RFC1213-MIB::ipRouteNextHop.127.0.0.0 = IpAddress: 127.0.0.1 RFC1213-MIB::ipRouteNextHop.172.16.0.0 = IpAddress: 172.16.149.242 RFC1213-MIB::ipRouteType.0.0.0.0 = INTEGER: indirect(4) RFC1213-MIB::ipRouteType.127.0.0.0 = INTEGER: direct(3) RFC1213-MIB::ipRouteType.172.16.0.0 = INTEGER: direct(3) RFC1213-MIB::ipRouteProto.0.0.0.0 = INTEGER: local(2) RFC1213-MIB::ipRouteProto.127.0.0.0 = INTEGER: local(2) RFC1213-MIB::ipRouteProto.172.16.0.0 = INTEGER: local(2) RFC1213-MIB::ipRouteAge.0.0.0.0 = INTEGER: 2840 RFC1213-MIB::ipRouteAge.127.0.0.0 = INTEGER: 10661 RFC1213-MIB::ipRouteAge.172.16.0.0 = INTEGER: 4284308 RFC1213-MIB::ipRouteMask.0.0.0.0 = IpAddress: 0.0.0.0 RFC1213-MIB::ipRouteMask.127.0.0.0 = IpAddress: 255.0.0.0 RFC1213-MIB::ipRouteMask.172.16.0.0 = IpAddress: 255.255.0.0 RFC1213-MIB::ipRouteMetric5.0.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric5.127.0.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteMetric5.172.16.0.0 = INTEGER: -1 RFC1213-MIB::ipRouteInfo.0.0.0.0 = OID: SNMPv2-SMI::zeroDotZero RFC1213-MIB::ipRouteInfo.127.0.0.0 = OID: SNMPv2-SMI::zeroDotZero RFC1213-MIB::ipRouteInfo.172.16.0.0 = OID: SNMPv2-SMI::zeroDotZero IP-MIB::ipNetToMediaIfIndex.2.172.16.0.2 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.3 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.4 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.5 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.6 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.7 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.8 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.9 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.10 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.11 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.12 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.13 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.14 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.15 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.16 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.17 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.18 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.19 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.20 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.21 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.22 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.23 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.24 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.25 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.26 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.27 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.28 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.29 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.30 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.0.31 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.10.1 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.10.2 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.10.20 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.100.1 = INTEGER: 2 IP-MIB::ipNetToMediaIfIndex.2.172.16.149.244 = INTEGER: 2 IP-MIB::ipRoutingDiscards.0 = Counter32: 0 IP-MIB::icmpInMsgs.0 = Counter32: 6421 IP-MIB::icmpInErrors.0 = Counter32: 0 IP-MIB::icmpInDestUnreachs.0 = Counter32: 6415 IP-MIB::icmpInTimeExcds.0 = Counter32: 0 IP-MIB::icmpInParmProbs.0 = Counter32: 0 IP-MIB::icmpInSrcQuenchs.0 = Counter32: 0 IP-MIB::icmpInRedirects.0 = Counter32: 0 IP-MIB::icmpInEchos.0 = Counter32: 6 IP-MIB::icmpInEchoReps.0 = Counter32: 0 IP-MIB::icmpInTimestamps.0 = Counter32: 0 IP-MIB::icmpInTimestampReps.0 = Counter32: 0 IP-MIB::icmpInAddrMasks.0 = Counter32: 0 IP-MIB::icmpInAddrMaskReps.0 = Counter32: 0 IP-MIB::icmpOutMsgs.0 = Counter32: 6 IP-MIB::icmpOutErrors.0 = Counter32: 0 IP-MIB::icmpOutDestUnreachs.0 = Counter32: 0 IP-MIB::icmpOutTimeExcds.0 = Counter32: 0 IP-MIB::icmpOutParmProbs.0 = Counter32: 0 IP-MIB::icmpOutSrcQuenchs.0 = Counter32: 0 IP-MIB::icmpOutRedirects.0 = Counter32: 0 IP-MIB::icmpOutEchos.0 = Counter32: 0 IP-MIB::icmpOutEchoReps.0 = Counter32: 6 IP-MIB::icmpOutTimestamps.0 = Counter32: 0 IP-MIB::icmpOutTimestampReps.0 = Counter32: 0 IP-MIB::icmpOutAddrMasks.0 = Counter32: 0 IP-MIB::icmpOutAddrMaskReps.0 = Counter32: 0 TCP-MIB::tcpRtoAlgorithm.0 = INTEGER: other(1) TCP-MIB::tcpRtoMin.0 = INTEGER: 1000 milliseconds TCP-MIB::tcpRtoMax.0 = INTEGER: 10000 milliseconds TCP-MIB::tcpMaxConn.0 = INTEGER: -1 TCP-MIB::tcpActiveOpens.0 = Counter32: 0 TCP-MIB::tcpPassiveOpens.0 = Counter32: 294 TCP-MIB::tcpAttemptFails.0 = Counter32: 0 TCP-MIB::tcpEstabResets.0 = Counter32: 0 TCP-MIB::tcpCurrEstab.0 = Gauge32: 0 TCP-MIB::tcpInSegs.0 = Counter32: 5336 TCP-MIB::tcpOutSegs.0 = Counter32: 4063 TCP-MIB::tcpRetransSegs.0 = Counter32: 11 TCP-MIB::tcpConnState.0.0.0.0.21.0.0.0.0.0 = INTEGER: listen(2) TCP-MIB::tcpConnState.0.0.0.0.23.0.0.0.0.0 = INTEGER: listen(2) TCP-MIB::tcpConnState.0.0.0.0.80.0.0.0.0.0 = INTEGER: listen(2) TCP-MIB::tcpConnLocalAddress.0.0.0.0.21.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnLocalAddress.0.0.0.0.23.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnLocalAddress.0.0.0.0.80.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnLocalPort.0.0.0.0.21.0.0.0.0.0 = INTEGER: 21 TCP-MIB::tcpConnLocalPort.0.0.0.0.23.0.0.0.0.0 = INTEGER: 23 TCP-MIB::tcpConnLocalPort.0.0.0.0.80.0.0.0.0.0 = INTEGER: 80 TCP-MIB::tcpConnRemAddress.0.0.0.0.21.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnRemAddress.0.0.0.0.23.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnRemAddress.0.0.0.0.80.0.0.0.0.0 = IpAddress: 0.0.0.0 TCP-MIB::tcpConnRemPort.0.0.0.0.21.0.0.0.0.0 = INTEGER: 0 TCP-MIB::tcpConnRemPort.0.0.0.0.23.0.0.0.0.0 = INTEGER: 0 TCP-MIB::tcpConnRemPort.0.0.0.0.80.0.0.0.0.0 = INTEGER: 0 TCP-MIB::tcpInErrs.0 = Counter32: 0 TCP-MIB::tcpOutRsts.0 = Counter32: 1 UDP-MIB::udpInDatagrams.0 = Counter32: 56992 UDP-MIB::udpNoPorts.0 = Counter32: 287 UDP-MIB::udpInErrors.0 = Counter32: 0 UDP-MIB::udpOutDatagrams.0 = Counter32: 64976 UDP-MIB::udpLocalAddress.0.0.0.0.68 = IpAddress: 0.0.0.0 UDP-MIB::udpLocalAddress.0.0.0.0.161 = IpAddress: 0.0.0.0 UDP-MIB::udpLocalAddress.0.0.0.0.1283 = IpAddress: 0.0.0.0 UDP-MIB::udpLocalAddress.0.0.0.0.2564 = IpAddress: 0.0.0.0 UDP-MIB::udpLocalAddress.0.0.0.0.12345 = IpAddress: 0.0.0.0 UDP-MIB::udpLocalPort.0.0.0.0.68 = INTEGER: 68 UDP-MIB::udpLocalPort.0.0.0.0.161 = INTEGER: 161 UDP-MIB::udpLocalPort.0.0.0.0.1283 = INTEGER: 1283 UDP-MIB::udpLocalPort.0.0.0.0.2564 = INTEGER: 2564 UDP-MIB::udpLocalPort.0.0.0.0.12345 = INTEGER: 12345 RFC1213-MIB::egpInMsgs.0 = Counter32: 0 RFC1213-MIB::egpInErrors.0 = Counter32: 0 RFC1213-MIB::egpOutMsgs.0 = Counter32: 0 RFC1213-MIB::egpOutErrors.0 = Counter32: 0 RFC1213-MIB::egpAs.0 = INTEGER: 0 SNMPv2-MIB::snmpInPkts.0 = Counter32: 56616 SNMPv2-MIB::snmpOutPkts.0 = Counter32: 56593 SNMPv2-MIB::snmpInBadVersions.0 = Counter32: 0 SNMPv2-MIB::snmpInBadCommunityNames.0 = Counter32: 23 SNMPv2-MIB::snmpInBadCommunityUses.0 = Counter32: 23 SNMPv2-MIB::snmpInASNParseErrs.0 = Counter32: 0 SNMPv2-MIB::snmpInTooBigs.0 = Counter32: 0 SNMPv2-MIB::snmpInNoSuchNames.0 = Counter32: 0 SNMPv2-MIB::snmpInBadValues.0 = Counter32: 0 SNMPv2-MIB::snmpInReadOnlys.0 = Counter32: 0 SNMPv2-MIB::snmpInGenErrs.0 = Counter32: 0 SNMPv2-MIB::snmpInTotalReqVars.0 = Counter32: 56608 SNMPv2-MIB::snmpInTotalSetVars.0 = Counter32: 0 SNMPv2-MIB::snmpInGetRequests.0 = Counter32: 4622 SNMPv2-MIB::snmpInGetNexts.0 = Counter32: 52008 SNMPv2-MIB::snmpInSetRequests.0 = Counter32: 0 SNMPv2-MIB::snmpInGetResponses.0 = Counter32: 0 SNMPv2-MIB::snmpInTraps.0 = Counter32: 0 SNMPv2-MIB::snmpOutTooBigs.0 = Counter32: 0 SNMPv2-MIB::snmpOutNoSuchNames.0 = Counter32: 11 SNMPv2-MIB::snmpOutBadValues.0 = Counter32: 0 SNMPv2-MIB::snmpOutGenErrs.0 = Counter32: 0 SNMPv2-MIB::snmpOutGetRequests.0 = Counter32: 0 SNMPv2-MIB::snmpOutGetNexts.0 = Counter32: 0 SNMPv2-MIB::snmpOutSetRequests.0 = Counter32: 0 SNMPv2-MIB::snmpOutGetResponses.0 = Counter32: 56617 SNMPv2-MIB::snmpOutTraps.0 = Counter32: 6644 SNMPv2-MIB::snmpEnableAuthenTraps.0 = INTEGER: enabled(1) SNMPv2-MIB::snmpSilentDrops.0 = Counter32: 0 SNMPv2-MIB::snmpProxyDrops.0 = Counter32: 0 SNMPv2-SMI::mib-2.33.1.1.1.0 = STRING: "Tripp Lite" SNMPv2-SMI::mib-2.33.1.1.2.0 = STRING: "SMART3000RM2U" SNMPv2-SMI::mib-2.33.1.1.3.0 = STRING: "1115 (Rev B)" SNMPv2-SMI::mib-2.33.1.1.4.0 = STRING: "12.03.0024" SNMPv2-SMI::mib-2.33.1.1.5.0 = STRING: "ups02" SNMPv2-SMI::mib-2.33.1.1.6.0 = "" SNMPv2-SMI::mib-2.33.1.2.4.0 = INTEGER: 100 SNMPv2-SMI::mib-2.33.1.2.5.0 = INTEGER: 54 SNMPv2-SMI::mib-2.33.1.2.7.0 = INTEGER: 31 SNMPv2-SMI::mib-2.33.1.3.1.0 = INTEGER: 0 SNMPv2-SMI::mib-2.33.1.3.2.0 = INTEGER: 1 SNMPv2-SMI::mib-2.33.1.3.3.1.1.1 = INTEGER: 0 SNMPv2-SMI::mib-2.33.1.3.3.1.3.1 = INTEGER: 121 SNMPv2-SMI::mib-2.33.1.4.1.0 = INTEGER: 3 SNMPv2-SMI::mib-2.33.1.4.3.0 = INTEGER: 1 SNMPv2-SMI::mib-2.33.1.4.4.1.1.1 = INTEGER: 0 SNMPv2-SMI::mib-2.33.1.4.4.1.5.1 = INTEGER: 67 SNMPv2-SMI::mib-2.33.1.5.2.0 = INTEGER: 0 -----Original Message----- From: Niels Baggesen [mailto:nba@users.sourceforge.net] Sent: Wednesday, March 01, 2006 2:20 AM To: Brady Chang Cc: nut-upsuser@lists.alioth.debian.org Subject: Re: [Nut-upsuser] tripplite SMART3000RM2U ups.status never change On Tue, Feb 28, 2006 at 08:46:41PM -0600, Brady Chang wrote:> > Hello, I was wonder if anybody experienced this problem or anyrecommendation on troubleshooting the problem.> unplug power, ups.status does not change. fedora core 4 kernel > 2.6.13-1.1532_FC4smp, binary compiled from latest 2.0.3 srcWhat does an snmpwalk of the ups show? /Niels -- Niels Baggesen - @home - ?rhus - Denmark - nba@users.sourceforge.net The purpose of computing is insight, not numbers --- R W Hamming