Ken Olum
2017-Dec-18 16:37 UTC
[Nut-upsuser] Tripp-Lite BCPERS450 shutdown/restart problems
I have a Tripp-Lite BCPERS450, connected to a system running Ubuntu 16.04.3 LTS and NUT 2.7.2-4ubuntu1.2. I had to make my own /lib/systemd/system-shutdown/nutshutdown, but now everything is working except for powering on and off the UPS. Regardless of the settings of offdelay and ondelay in upsconf, and regardless of whether the AC power is on, when I say "upsdrvctl shutdown" the UPS turns off the power to the system instantly and turns it back on in ten seconds. Any ideas how to get more reasonable behavior, in particular not turning the system back on until the AC power is restored? Here is the status reported by upsc: battery.charge: 100 battery.runtime: 4050 battery.type: PbAC battery.voltage: 13.4 battery.voltage.nominal: 12.0 device.mfr: Tripp Lite device.model: Tripp Lite UPS device.type: ups driver.name: usbhid-ups driver.parameter.offdelay: 20 driver.parameter.ondelay: -1 driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.7.2 driver.version.data: TrippLite HID 0.81 driver.version.internal: 0.38 input.frequency: 60.0 input.voltage: 118.2 input.voltage.nominal: 120 output.frequency.nominal: 60 output.voltage.nominal: 120 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.mfr: Tripp Lite ups.model: Tripp Lite UPS ups.power.nominal: 450 ups.productid: 2010 ups.status: OL ups.timer.reboot: 65535 ups.timer.shutdown: 65535 ups.vendorid: 09ae ups.watchdog.status: 0 I said /lib/nut/usbhid-ups -DD -a bcpers450 and got: Network UPS Tools - Generic HID driver 0.38 (2.7.2) USB communication driver 0.32 0.000000 debug level is '2' 0.000808 upsdrv_initups... 0.017090 Checking device (1D6B/0003) (002/001) 0.033199 - VendorID: 1d6b 0.033215 - ProductID: 0003 0.033217 - Manufacturer: unknown 0.033220 - Product: unknown 0.033222 - Serial Number: unknown 0.033224 - Bus: 002 0.033227 Trying to match device 0.033232 Device does not match - skipping 0.033289 Checking device (09AE/2010) (001/014) 0.036998 - VendorID: 09ae 0.037011 - ProductID: 2010 0.037014 - Manufacturer: Tripp Lite 0.037018 - Product: Tripp Lite UPS 0.037021 - Serial Number: unknown 0.037024 - Bus: 001 0.037027 Trying to match device 0.037042 Device matches 0.037886 HID descriptor too short (expected 8, got 0) 0.037901 HID descriptor length 613 0.057332 Report Descriptor size = 613 0.057663 Using subdriver: TrippLite HID 0.81 0.058304 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 2 0.059008 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 3 0.059619 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 1 0.060167 Path: UPS.PowerSummary.ffff00d9, Type: Feature, ReportID: 0xc0, Offset: 0, Size: 8, Value: 5 0.060709 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120 0.061316 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.061905 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4 0.062534 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2 0.063079 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1 0.063619 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050 0.063658 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050 0.064254 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.064292 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.064954 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100 0.065578 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100 0.066133 Path: UPS.PowerSummary.PresentStatus.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 1182 0.066673 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.066711 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 0.066736 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 to 0.066756 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 0.066777 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.066798 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.066819 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.066839 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.066863 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.066886 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 0.066908 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 0.066931 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 0.066953 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.066977 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.067000 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.067022 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.067583 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12 0.068064 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 0, Size: 1, Value: 1 0.068087 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 1, Size: 1, Value: 0 0.068108 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0 0.068625 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.069120 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120 0.069695 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60 0.070252 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450 0.070916 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.071567 Path: UPS.OutletSystem.Outlet.ffff00bc, Type: Feature, ReportID: 0xe0, Offset: 0, Size: 16, Value: 0 0.072081 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 0 0.072701 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.073273 Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, ReportID: 0xb6, Offset: 0, Size: 8, Value: 1 0.073997 Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type: Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 8208 0.074644 Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, Offset: 0, Size: 8, Value: 255 0.075266 refresh_report_buffer: expected 5 bytes, but got 2 instead 0.075310 Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, Offset: 0, Size: 32, Value: 255 0.075908 refresh_report_buffer: expected 5 bytes, but got 2 instead 0.075952 Path: UPS.ffff0015.[1].ffff00d3, Type: Feature, ReportID: 0xb5, Offset: 0, Size: 32, Value: 255 0.076633 Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, Offset: 0, Size: 16, Value: 255 0.077150 Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, Offset: 0, Size: 8, Value: 255 0.077710 Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, Offset: 0, Size: 16, Value: 255 0.078289 Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, Offset: 0, Size: 16, Value: 3 0.079011 Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, Size: 32, Value: 14 0.079620 libusb_get_report: error sending control message: Operation not permitted 0.079665 Can't retrieve Report c1: Operation not permitted 0.079687 Path: UPS.ffff0015.[1].ffff00d8, Type: Feature, ReportID: 0xc1, Offset: 0, Size: 32 0.080267 Path: UPS.ffff0015.[1].ffff00d7, Type: Feature, ReportID: 0xc3, Offset: 0, Size: 32, Value: 1 0.080847 libusb_get_report: error sending control message: Operation not permitted 0.080879 Can't retrieve Report 9a: Operation not permitted 0.080937 Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0, Size: 32 0.081647 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 134 0.082228 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 118.2 0.083058 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 60 0.083646 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0 0.083681 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0 0.083704 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0 0.083723 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0 0.083741 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, Offset: 5, Size: 1, Value: 0 0.083758 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0 0.083777 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0 0.083799 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0 0.084531 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.084569 Report descriptor retrieved (Reportlen = 613) 0.084578 Found HID device 0.084591 Detected a UPS: Tripp Lite /Tripp Lite UPS 0.084664 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.084726 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050 0.084748 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12 0.084772 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 134 0.084795 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4 0.086130 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.086156 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.086175 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.086201 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.086224 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450 0.086272 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.086305 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.086325 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 0.086346 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.086365 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.086385 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 0.086402 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 0.086420 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.086439 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.086486 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 0 0.086508 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0 0.086527 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0 0.086546 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0 0.086565 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0 0.086583 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0 0.086603 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0 0.086622 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120 0.086651 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 118.2 0.086672 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 60 0.086722 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120 0.086756 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60 0.086781 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.086797 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.086813 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.086834 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.086862 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.086881 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.086897 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.086912 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.086928 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.086944 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.086960 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.086975 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.086990 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.087010 find_nut_info: unknown info type: load.on.delay 0.087022 find_nut_info: unknown info type: load.on.delay 0.087041 upsdrv_initinfo... 0.087055 upsdrv_updateinfo... 0.338069 libusb_get_interrupt: Connection timed out 0.338103 Got 0 HID objects... 0.338178 Quick update... 0.338215 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.338242 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.338262 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 0.338277 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.338303 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.338337 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 0.338352 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 0.338373 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.338503 dstate_init: sock /var/run/nut/usbhid-ups-bcpers450 open on fd 5 0.338534 upsdrv_updateinfo... 0.343549 Got 1 HID objects... 0.343585 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 4050 0.343603 Quick update... 0.343628 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.343632 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.343636 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 0.343639 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.343642 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.343645 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 0.343647 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 0.343650 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 2.340759 upsdrv_updateinfo... 2.359621 Got 8 HID objects... 2.359637 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 2.359646 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 2.359653 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 2.359659 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 2.359665 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 2.359672 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 2.359677 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 2.359683 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 2.359690 Quick update... 2.360150 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 2.360609 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 2.360614 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 1 2.360617 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 2.360620 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 2.360623 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 1 2.360625 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 0 2.360628 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 Thanks very much. Ken
Charles Lepple
2017-Dec-19 00:26 UTC
[Nut-upsuser] Tripp-Lite BCPERS450 shutdown/restart problems
[please use reply-all to post to the list - the mailing list does not add a reply-to header. thanks!] On Dec 18, 2017, at 11:37 AM, Ken Olum wrote:> > I have a Tripp-Lite BCPERS450, connected to a system running Ubuntu > 16.04.3 LTS and NUT 2.7.2-4ubuntu1.2. I had to make my own > /lib/systemd/system-shutdown/nutshutdown, but now everything is working > except for powering on and off the UPS. Regardless of the settings of > offdelay and ondelay in upsconf, and regardless of whether the AC power > is on, when I say "upsdrvctl shutdown" the UPS turns off the power to > the system instantly and turns it back on in ten seconds.Thanks for the specific version info and detailed logs. This may sound like an apples-to-oranges comparison, but we did uncover an issue with CyberPower UPSes where the delay values needed to be greater than or equal to 60 (seconds), since they were being rounded down to integer numbers of minutes internally: https://github.com/networkupstools/nut/issues/432 What was the largest delay you tried?> ups.timer.reboot: 65535 > ups.timer.shutdown: 65535 >I can't test this on either one of my Tripp-Lite units (one is too old, and the other has the ill-fated 3016 protocol USB controller that can't stay on the bus long enough to do anything useful), but I seem to remember that these values should change to e.g. -60 if you set the delay to 60, and then they should begin counting down after the shutdown command is sent. It has been a while since I messed with that code, though. What log messages do you get with "/lib/nut/usbhid-ups -DD -a bcpers450 -k"? (NOTE this will also tell the UPS to shut down immediately - it's the command that upsdrvctl runs, but with more debugging.) For future reference, was this UPS manufactured recently? The NUT source code mentions that the TLCustom prefix is 0xffff0010, but the HID descriptor dump shows a few items under "UPS.ffff0015". Hopefully the delays haven't been moved to those values, since we don't have good information on the corresponding names. Also, it may be worthwhile to reach out to Tripp Lite support. A few years ago, the NUT project got a large spreadsheet of testing results (mostly upsc output, rather than full end-to-end) from connecting many of their their USB UPS models to NUT from one of their sales offices. Interestingly, the following models have the same USB product ID as your UPS, and the Smart1000LCD was on that list: * http://networkupstools.org/ddl/Tripp_Lite/AVR900U.html * http://networkupstools.org/ddl/Tripp_Lite/G1010USB.html * http://networkupstools.org/ddl/Tripp_Lite/SMART1000LCD.html> _______________________________________________ > Nut-upsuser mailing list > Nut-upsuser at lists.alioth.debian.org > http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
Ken Olum
2017-Dec-20 15:32 UTC
[Nut-upsuser] Tripp-Lite BCPERS450 shutdown/restart problems
Thanks for your help. From: Charles Lepple <clepple at gmail.com> Date: Mon, 18 Dec 2017 19:26:56 -0500 This may sound like an apples-to-oranges comparison, but we did uncover an issue with CyberPower UPSes where the delay values needed to be greater than or equal to 60 (seconds), since they were being rounded down to integer numbers of minutes internally: What was the largest delay you tried? I have now tried 200 seconds without any change. The offdelay setting does appear in the status as ups.delay.shutdown, but seems to have no effect. > ups.timer.reboot: 65535 > ups.timer.shutdown: 65535 > I seem to remember that these values should change to e.g. -60 if you set the delay to 60, and then they should begin counting down after the shutdown command is sent. It has been a while since I messed with that code, though. No matter what settings I use, the UPS seems to turn off the load immediately in response to the shutdown command. I have never seen ups.timer.shutdown change from the value above. After shutting off the load, ups.timer.reboot changes to 10, regardless of the setting of driver.parameter.ondelay. It then counts down to 0 and turns the load back on. What log messages do you get with "/lib/nut/usbhid-ups -DD -a bcpers450 -k"? See below. For future reference, was this UPS manufactured recently? I have just purchased it new, so presumably yes. Ken ---------------------------------------------------------------------- # /lib/nut/usbhid-ups -DD -a bcpers450 -k Network UPS Tools - Generic HID driver 0.38 (2.7.2) USB communication driver 0.32 0.000000 debug level is '2' 0.000852 upsdrv_initups... 0.014448 Checking device (1D6B/0003) (002/001) 0.030206 - VendorID: 1d6b 0.030219 - ProductID: 0003 0.030239 - Manufacturer: unknown 0.030242 - Product: unknown 0.030246 - Serial Number: unknown 0.030249 - Bus: 002 0.030253 Trying to match device 0.030259 Device does not match - skipping 0.030304 Checking device (09AE/2010) (001/009) 0.034107 - VendorID: 09ae 0.034120 - ProductID: 2010 0.034122 - Manufacturer: Tripp Lite 0.034153 - Product: Tripp Lite UPS 0.034156 - Serial Number: unknown 0.034159 - Bus: 001 0.034162 Trying to match device 0.034179 Device matches 0.034195 failed to claim USB device: could not claim interface 0: Device or resource busy 0.034209 detached kernel driver from USB device... 0.035773 HID descriptor length 613 0.054980 Report Descriptor size = 613 0.055190 Using subdriver: TrippLite HID 0.81 0.055810 Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 0x28, Offset: 0, Size: 8, Value: 2 0.056434 Path: UPS.PowerSummary.iSerialNumber, Type: Feature, ReportID: 0x29, Offset: 0, Size: 8, Value: 3 0.056913 Path: UPS.PowerSummary.iManufacturer, Type: Feature, ReportID: 0x2b, Offset: 0, Size: 8, Value: 1 0.057431 Path: UPS.PowerSummary.ffff00d9, Type: Feature, ReportID: 0xc0, Offset: 0, Size: 8, Value: 5 0.057855 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120 0.058533 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.059163 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4 0.059667 Path: UPS.PowerSummary.CapacityMode, Type: Feature, ReportID: 0x33, Offset: 0, Size: 8, Value: 2 0.060193 Path: UPS.PowerSummary.Rechargeable, Type: Feature, ReportID: 0x2c, Offset: 0, Size: 8, Value: 1 0.060733 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, ReportID: 0x35, Offset: 0, Size: 16, Value: 5740 0.060755 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 5740 0.061271 Path: UPS.PowerSummary.RemainingCapacity, Type: Input, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.061291 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.061896 Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, ReportID: 0x37, Offset: 0, Size: 8, Value: 100 0.062368 Path: UPS.PowerSummary.DesignCapacity, Type: Feature, ReportID: 0x36, Offset: 0, Size: 8, Value: 100 0.062904 Path: UPS.PowerSummary.PresentStatus.Voltage, Type: Feature, ReportID: 0x31, Offset: 0, Size: 16, Value: 0 0.063470 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Input, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.063512 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Input, ReportID: 0x32, Offset: 1, Size: 1, Value: 0 0.063539 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, ReportID: 0x32, Offset: 2, Size: 1, Value: 0 0.063558 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Input, ReportID: 0x32, Offset: 3, Size: 1, Value: 1 0.063577 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Input, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.063595 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.063616 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Input, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.063636 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Input, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.063657 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.063679 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 0 0.063703 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 0 0.063727 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 1 0.063749 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.063769 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.063792 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.063814 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.064263 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12 0.064738 Path: UPS.BatterySystem.Battery.PresentStatus.Charging, Type: Feature, ReportID: 0x23, Offset: 0, Size: 1, Value: 0 0.064761 Path: UPS.BatterySystem.Battery.PresentStatus.Discharging, Type: Feature, ReportID: 0x23, Offset: 1, Size: 1, Value: 1 0.064782 Path: UPS.BatterySystem.Battery.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x23, Offset: 2, Size: 1, Value: 0 0.065251 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.065790 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120 0.066320 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60 0.066955 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450 0.067583 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.068231 Path: UPS.OutletSystem.Outlet.ffff00bc, Type: Feature, ReportID: 0xe0, Offset: 0, Size: 16, Value: 0 0.068757 Path: UPS.OutletSystem.Outlet.ffff0091, Type: Feature, ReportID: 0x51, Offset: 0, Size: 8, Value: 1 0.069251 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.069779 Path: UPS.OutletSystem.Outlet.ffff00c7, Type: Feature, ReportID: 0xb6, Offset: 0, Size: 8, Value: 1 0.070327 Path: UPS.TLCustom.[1].CommunicationProtocolVersion, Type: Feature, ReportID: 0x6c, Offset: 0, Size: 16, Value: 8208 0.070953 Path: UPS.ffff0015.[1].ffff00c0, Type: Feature, ReportID: 0x96, Offset: 0, Size: 8, Value: 255 0.071418 refresh_report_buffer: expected 5 bytes, but got 2 instead 0.071462 Path: UPS.ffff0015.[1].ffff00d2, Type: Feature, ReportID: 0xb4, Offset: 0, Size: 32, Value: 255 0.072034 refresh_report_buffer: expected 5 bytes, but got 2 instead 0.072077 Path: UPS.ffff0015.[1].ffff00d3, Type: Feature, ReportID: 0xb5, Offset: 0, Size: 32, Value: 255 0.072671 Path: UPS.ffff0015.[1].ffff00c1, Type: Feature, ReportID: 0x97, Offset: 0, Size: 16, Value: 255 0.073152 Path: UPS.ffff0015.[1].ffff00c2, Type: Feature, ReportID: 0x98, Offset: 0, Size: 8, Value: 255 0.073668 Path: UPS.ffff0015.[1].ffff00c3, Type: Feature, ReportID: 0x99, Offset: 0, Size: 16, Value: 255 0.078695 Path: UPS.ffff0015.[1].ffff00c5, Type: Feature, ReportID: 0x9b, Offset: 0, Size: 16, Value: 3 0.079245 Path: UPS.ffff0015.[1].ffff00d6, Type: Feature, ReportID: 0xc2, Offset: 0, Size: 32, Value: 14 0.079703 libusb_get_report: could not claim interface 0: Device or resource busy 0.079755 Can't retrieve Report c1: Device or resource busy 0.079781 Path: UPS.ffff0015.[1].ffff00d8, Type: Feature, ReportID: 0xc1, Offset: 0, Size: 32 0.080340 Path: UPS.ffff0015.[1].ffff00d7, Type: Feature, ReportID: 0xc3, Offset: 0, Size: 32, Value: 1 0.080865 libusb_get_report: could not claim interface 0: Device or resource busy 0.080897 Can't retrieve Report 9a: Device or resource busy 0.080919 Path: UPS.ffff0015.[1].ffff00c4, Type: Feature, ReportID: 0x9a, Offset: 0, Size: 32 0.081587 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 124 0.082168 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0 0.082724 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 0 0.083265 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 1 0.083304 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0 0.083327 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0 0.083349 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0 0.083368 Path: UPS.PowerConverter.PresentStatus.Used, Type: Feature, ReportID: 0x22, Offset: 5, Size: 1, Value: 0 0.083388 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0 0.083408 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0 0.083427 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0 0.083917 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.083952 Report descriptor retrieved (Reportlen = 613) 0.083962 Found HID device 0.083975 Detected a UPS: Tripp Lite /Tripp Lite UPS 0.084049 Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, ReportID: 0x34, Offset: 0, Size: 8, Value: 100 0.084108 Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, ReportID: 0x35, Offset: 0, Size: 16, Value: 5740 0.084137 Path: UPS.BatterySystem.Battery.ConfigVoltage, Type: Feature, ReportID: 0x04, Offset: 0, Size: 16, Value: 12 0.084166 Path: UPS.BatterySystem.Battery.Voltage, Type: Feature, ReportID: 0x20, Offset: 0, Size: 16, Value: 124 0.084196 Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, ReportID: 0x2a, Offset: 0, Size: 8, Value: 4 0.085345 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.085377 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.085404 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.085426 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.085453 Path: UPS.Flow.ConfigApparentPower, Type: Feature, ReportID: 0x03, Offset: 0, Size: 16, Value: 450 0.085507 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.085546 Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, Type: Feature, ReportID: 0x32, Offset: 0, Size: 1, Value: 0 0.085573 Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: Feature, ReportID: 0x32, Offset: 1, Size: 1, Value: 0 0.085598 Path: UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, ReportID: 0x32, Offset: 5, Size: 1, Value: 0 0.085623 Path: UPS.PowerSummary.PresentStatus.FullyCharged, Type: Feature, ReportID: 0x32, Offset: 6, Size: 1, Value: 1 0.085648 Path: UPS.PowerSummary.PresentStatus.Charging, Type: Feature, ReportID: 0x32, Offset: 2, Size: 1, Value: 0 0.085672 Path: UPS.PowerSummary.PresentStatus.Discharging, Type: Feature, ReportID: 0x32, Offset: 3, Size: 1, Value: 1 0.085696 Path: UPS.PowerSummary.PresentStatus.FullyDischarged, Type: Feature, ReportID: 0x32, Offset: 7, Size: 1, Value: 0 0.085720 Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: Feature, ReportID: 0x32, Offset: 4, Size: 1, Value: 0 0.085770 Path: UPS.PowerConverter.PresentStatus.VoltageOutOfRange, Type: Feature, ReportID: 0x22, Offset: 0, Size: 1, Value: 1 0.085795 Path: UPS.PowerConverter.PresentStatus.Buck, Type: Feature, ReportID: 0x22, Offset: 1, Size: 1, Value: 0 0.085819 Path: UPS.PowerConverter.PresentStatus.Boost, Type: Feature, ReportID: 0x22, Offset: 2, Size: 1, Value: 0 0.085843 Path: UPS.PowerConverter.PresentStatus.Overload, Type: Feature, ReportID: 0x22, Offset: 4, Size: 1, Value: 0 0.085866 Path: UPS.PowerConverter.PresentStatus.OverTemperature, Type: Feature, ReportID: 0x22, Offset: 6, Size: 1, Value: 0 0.085890 Path: UPS.PowerConverter.PresentStatus.InternalFailure, Type: Feature, ReportID: 0x22, Offset: 7, Size: 1, Value: 0 0.085913 Path: UPS.PowerConverter.PresentStatus.AwaitingPower, Type: Feature, ReportID: 0x22, Offset: 14, Size: 1, Value: 0 0.085937 Path: UPS.PowerSummary.Input.ConfigVoltage, Type: Feature, ReportID: 0x30, Offset: 0, Size: 8, Value: 120 0.085972 Path: UPS.PowerConverter.Input.Voltage, Type: Feature, ReportID: 0x18, Offset: 0, Size: 16, Value: 0 0.085997 Path: UPS.PowerConverter.Input.Frequency, Type: Feature, ReportID: 0x19, Offset: 0, Size: 16, Value: 0 0.086053 Path: UPS.Flow.ConfigVoltage, Type: Feature, ReportID: 0x01, Offset: 0, Size: 8, Value: 120 0.086094 Path: UPS.Flow.ConfigFrequency, Type: Feature, ReportID: 0x02, Offset: 0, Size: 8, Value: 60 0.090270 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.090329 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.090349 Path: UPS.BatterySystem.Test, Type: Feature, ReportID: 0x10, Offset: 0, Size: 8, Value: 0 0.090375 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.090407 Path: UPS.OutletSystem.Outlet.DelayBeforeShutdown, Type: Feature, ReportID: 0x15, Offset: 0, Size: 16, Value: 65535 0.090426 Path: UPS.OutletSystem.Outlet.DelayBeforeReboot, Type: Feature, ReportID: 0x17, Offset: 0, Size: 16, Value: 65535 0.090443 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.090458 Path: UPS.OutletSystem.Outlet.TLWatchdog, Type: Feature, ReportID: 0x52, Offset: 0, Size: 8, Value: 0 0.090477 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.090493 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.090508 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.090523 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.090539 Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, ReportID: 0x11, Offset: 0, Size: 8, Value: 2 0.090564 find_nut_info: unknown info type: load.on.delay 0.090577 find_nut_info: unknown info type: load.on.delay 0.090585 Initiating UPS shutdown 0.090593 upsdrv_shutdown... 0.090601 instcmd(shutdown.return, [NULL]) 0.090614 find_nut_info: unknown info type: shutdown.return 0.090624 instcmd(load.on.delay, [NULL]) 0.090633 find_nut_info: unknown info type: load.on.delay 0.090641 instcmd: info element unavailable load.on.delay 0.090649 instcmd(shutdown.reboot, [NULL]) 0.091107 upsdrv_cleanup...
Reasonably Related Threads
- Tripp Lite SMART1500LCD will not stay shut down when power is disconnected
- Tripp-Lite BCPERS450 shutdown/restart problems
- Tripp Lite SMART1500LCD repeatedly disconnecting and reconnecting
- TrippLite SMART1500LCD no delay before ups shutdown.
- Crash when I start driver