Charles Lepple
2014-Aug-08 13:15 UTC
[Nut-upsuser] Cyberpower Value1200E might not need 0.667 battery scaling
On Aug 7, 2014, at 10:52 PM, Charles Lepple <clepple at gmail.com> wrote:> On Aug 7, 2014, at 10:18 PM, Matthew Stapleton <matthew4196 at gmail.com> wrote: > >> I just got a Cyberpower SOHO Value 1200 ELCD UPS and even with nut 2.7.2, it appears to report battery voltage too low due to the battery scaling function (In drivers/cps-hid.c). Even though the ups has usb id: 0764:0501, UPS.PowerSummary.Voltage reports 26.6 for the 24V batteries so when the 0.667 battery scale is applied that goes down to 17.7V. > > I'm wondering if that scale factor is only needed for that one Dynex UPS model. We should be able to do a string match, which is ugly, but should work (especially if we default to no scaling). > > Logged: https://github.com/networkupstools/nut/issues/142It's not just Dynex models - there are some early "UPS VALUE" and "CP 1000D" units that seem to need the correction factor. I'll try to add a check that looks to see if the battery voltage makes sense. -- Charles Lepple clepple at gmail
Charles Lepple
2014-Aug-09 15:27 UTC
[Nut-upsuser] Cyberpower Value1200E might not need 0.667 battery scaling
On Aug 8, 2014, at 9:15 AM, Charles Lepple <clepple at gmail.com> wrote:> On Aug 7, 2014, at 10:52 PM, Charles Lepple <clepple at gmail.com> wrote: > >> On Aug 7, 2014, at 10:18 PM, Matthew Stapleton <matthew4196 at gmail.com> wrote: >> >>> I just got a Cyberpower SOHO Value 1200 ELCD UPS and even with nut 2.7.2, it appears to report battery voltage too low due to the battery scaling function (In drivers/cps-hid.c). Even though the ups has usb id: 0764:0501, UPS.PowerSummary.Voltage reports 26.6 for the 24V batteries so when the 0.667 battery scale is applied that goes down to 17.7V. >> >> I'm wondering if that scale factor is only needed for that one Dynex UPS model. We should be able to do a string match, which is ugly, but should work (especially if we default to no scaling). >> >> Logged: https://github.com/networkupstools/nut/issues/142 > > It's not just Dynex models - there are some early "UPS VALUE" and "CP 1000D" units that seem to need the correction factor. I'll try to add a check that looks to see if the battery voltage makes sense.Matthew, can you try the attached patch, and run the driver it with -DDDD? https://github.com/networkupstools/nut/commit/c8950dee9c91ce45d05d8f220ea26891fb92329e Also, if anyone else has a Cyberpower UPS with the 0501 productID, I'd appreciate any additional testing. Thanks, -- Charles Lepple clepple at gmail -------------- next part -------------- A non-text attachment was scrubbed... Name: cps_hid_scale.patch Type: application/octet-stream Size: 3286 bytes Desc: not available URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20140809/6eb8b9a0/attachment.obj>
Matthew Stapleton
2014-Aug-11 01:29 UTC
[Nut-upsuser] Cyberpower Value1200E might not need 0.667 battery scaling
Attached is the first 32 seconds of the driver output after applying the patch which fixes the battery scaling problem for this UPS. Matthew Stapleton Email: matthew4196 at gmail.com On 10/08/14 01:27, Charles Lepple wrote:> On Aug 8, 2014, at 9:15 AM, Charles Lepple <clepple at gmail.com> wrote: > >> On Aug 7, 2014, at 10:52 PM, Charles Lepple <clepple at gmail.com> wrote: >> >>> On Aug 7, 2014, at 10:18 PM, Matthew Stapleton <matthew4196 at gmail.com> wrote: >>> >>>> I just got a Cyberpower SOHO Value 1200 ELCD UPS and even with nut 2.7.2, it appears to report battery voltage too low due to the battery scaling function (In drivers/cps-hid.c). Even though the ups has usb id: 0764:0501, UPS.PowerSummary.Voltage reports 26.6 for the 24V batteries so when the 0.667 battery scale is applied that goes down to 17.7V. >>> I'm wondering if that scale factor is only needed for that one Dynex UPS model. We should be able to do a string match, which is ugly, but should work (especially if we default to no scaling). >>> >>> Logged: https://github.com/networkupstools/nut/issues/142 >> It's not just Dynex models - there are some early "UPS VALUE" and "CP 1000D" units that seem to need the correction factor. I'll try to add a check that looks to see if the battery voltage makes sense. > Matthew, can you try the attached patch, and run the driver it with -DDDD? > > https://github.com/networkupstools/nut/commit/c8950dee9c91ce45d05d8f220ea26891fb92329e > > Also, if anyone else has a Cyberpower UPS with the 0501 productID, I'd appreciate any additional testing. > > Thanks, > > > cps_hid_scale.patch > > > commit c8950dee9c91ce45d05d8f220ea26891fb92329e > Author: Charles Lepple <clepple+nut at gmail.com> > Date: Sat Aug 9 11:19:27 2014 -0400 > > usbhid-ups (CPS): determine battery.voltage scale factor at runtime > > If the battery.voltage reading is greater than 1.4x battery.voltage.nominal, > apply a scale factor of 2/3 to bring the voltage back in line. > > Closes networkupstools/nut#142 > > diff --git a/drivers/cps-hid.c b/drivers/cps-hid.c > index a6d64ba..78c952f 100644 > --- a/drivers/cps-hid.c > +++ b/drivers/cps-hid.c > @@ -28,29 +28,36 @@ > #include "cps-hid.h" > #include "usb-common.h" > > -#define CPS_HID_VERSION "CyberPower HID 0.3" > +#define CPS_HID_VERSION "CyberPower HID 0.4" > > /* Cyber Power Systems */ > #define CPS_VENDORID 0x0764 > > -/* > +/*! Battery voltage scale factor. > * For some devices, the reported battery voltage is off by factor > * of 1.5 so we need to apply a scale factor to it to get the real > * battery voltage. By default, the factor is 1 (no scaling). > */ > static double battery_scale = 1; > +static int might_need_battery_scale = 0; > +static int battery_scale_checked = 0; > + > +/*! If the ratio of the battery voltage to the nominal battery voltage exceeds > + * this factor, we assume that the battery voltage needs to be scaled by 2/3. > + */ > +static const double battery_voltage_sanity_check = 1.4; > > static void *cps_battery_scale(USBDevice_t *device) > { > - battery_scale = 0.667; > + might_need_battery_scale = 1; > return NULL; > } > > /* USB IDs device table */ > static usb_device_id_t cps_usb_device_table[] = { > - /* 900AVR/BC900D, CP1200AVR/BC1200D */ > + /* 900AVR/BC900D */ > { USB_DEVICE(CPS_VENDORID, 0x0005), NULL }, > - /* Dynex DX-800U? */ > + /* Dynex DX-800U?, CP1200AVR/BC1200D, CP825AVR-G, CP1000AVRLCD, CP1000PFCLCD, CP1500C, CP550HG, etc. */ > { USB_DEVICE(CPS_VENDORID, 0x0501), &cps_battery_scale }, > /* OR2200LCDRM2U, OR700LCDRM1U, PR6000LCDRTXL5U */ > { USB_DEVICE(CPS_VENDORID, 0x0601), NULL }, > @@ -59,12 +66,48 @@ static usb_device_id_t cps_usb_device_table[] = { > { -1, -1, NULL } > }; > > +/*! Adjusts @a battery_scale if voltage is well above nominal. > + */ > +static void cps_adjust_battery_scale(double batt_volt) > +{ > + const char *batt_volt_nom_str; > + double batt_volt_nom; > + > + if(battery_scale_checked) { > + return; > + } > + > + batt_volt_nom_str = dstate_getinfo("battery.voltage.nominal"); > + if(!batt_volt_nom_str) { > + upsdebugx(2, "%s: 'battery.voltage.nominal' not available yet; skipping scale determination", __func__); > + return; > + } > + > + batt_volt_nom = strtod(batt_volt_nom_str, NULL); > + if(batt_volt_nom == 0) { > + upsdebugx(3, "%s: 'battery.voltage.nominal' is %s", __func__, batt_volt_nom_str); > + return; > + } > + > + if( (batt_volt / batt_volt_nom) > battery_voltage_sanity_check ) { > + upslogx(LOG_INFO, "%s: battery readings will be scaled by 2/3", __func__); > + battery_scale = 2.0/3; > + } > + > + battery_scale_checked = 1; > +} > + > /* returns statically allocated string - must not use it again before > done with result! */ > static const char *cps_battvolt_fun(double value) > { > static char buf[8]; > > + if(might_need_battery_scale) { > + cps_adjust_battery_scale(value); > + } > + > + upsdebugx(5, "%s: battery_scale = %.3f", __func__, battery_scale); > snprintf(buf, sizeof(buf), "%.1f", battery_scale * value); > > return buf;-------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20140811/86140247/attachment.html> -------------- next part -------------- A non-text attachment was scrubbed... Name: cyberpower_debug_log.txt.gz Type: application/x-gzip Size: 6728 bytes Desc: not available URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20140811/86140247/attachment.bin>
Possibly Parallel Threads
- Cyberpower Value1200E might not need 0.667 battery scaling
- Cyberpower Value1200E might not need 0.667 battery scaling
- Cyberpower Value1200E might not need 0.667 battery scaling
- Cyberpower Value1200E might not need 0.667 battery scaling
- TrippLite SMART1000LCD