Hi Installed new APC Back-UPS CS 350 on single server running openSUSE 11.2 64-bit and configured NUT 2.4.1 (SUSE package) according to instructions. When testing, NUT shuts down the server correctly and instructs the UPS to power down. UPS does so after some 20s delay, everything without errors. But after restoring main power, even after waiting for 1/2h UPS does not by itself turn on again, all LEDs are dark. One has to manually press the UPS's power button, which makes server and monitor run again immediately. What could be wrong that prevents UPS from turning itself on again? Below output of upsc: battery.charge: 95 battery.charge.low: 10 battery.charge.warning: 50 battery.date: 2009/10/11 battery.mfr.date: 2009/10/11 battery.runtime: 1237 battery.runtime.low: 180 battery.temperature: 29.2 battery.type: PbAc battery.voltage: 13.6 battery.voltage.nominal: 12.0 driver.name: usbhid-ups driver.parameter.pollfreq: 30 driver.parameter.pollinterval: 2 driver.parameter.port: auto driver.version: 2.4.1 driver.version.data: APC HID 0.93 driver.version.internal: 0.34 input.voltage: 122.0 input.voltage.nominal: 120 output.voltage: 115.0 output.voltage.nominal: 120.0 ups.beeper.status: enabled ups.delay.shutdown: 20 ups.firmware: 805.q8.D ups.firmware.aux: q8 ups.load: 49.0 ups.mfr: American Power Conversion ups.mfr.date: 2009/10/11 ups.model: Back-UPS CS 350 ups.productid: 0002 ups.serial: 4B0941P71480 ups.status: OL CHRG ups.test.result: No test initiated ups.timer.reboot: 0 ups.timer.shutdown: -1 ups.vendorid: 051d Thanks a lot for any hint! -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://lists.alioth.debian.org/pipermail/nut-upsuser/attachments/20091222/8b934c58/attachment.htm>
Arjen de Korte
2009-Dec-22 22:15 UTC
[Nut-upsuser] APC UPS won't restart after power outage
Citeren Ole Hoppe <ole.hoppe op gmail.com>:> What could be wrong that prevents UPS from turning itself on again?The UPS might not support this, in which case there is nothing we can do about this. The APC Back-UPS CS 350 is an entry level consumer grade UPS which is intended to power small desktop systems (not a server running unattended). If you want to find out what is happening under the hood, you could run the driver in debug mode (not powering the server, since the output *will* be switched off without warning during this test). Stop NUT before running the below command: /path/to/usbhid-ups -DDD -k -a <upsname> With mains present, this will most likely cycle the mains. Since the UPS doesn't support a startup with delay, I guess it will turn off the load and stay off in the absence of mains voltage. Best regards, Arjen -- Please keep list traffic on the list
Apparently Analagous Threads
- after power outage and proper shutdown, UPS turns on before power returns
- after power outage and proper shutdown, UPS turns on before power returns
- Gracefully powering off system in case of power failure
- after power outage and proper shutdown, UPS turns on before power returns
- Synology NAS is shutting down Ubuntu servers after very brief power outage (fwd)